Replacing DC drive

joe75140

Member
Join Date
Aug 2006
Location
Tennessee
Posts
27
Hi, we are replacing an old Reliance DC drive with a Quantum 3 drive. The motor has a 240 vdc armature. The iso transformer for the drive is 480 vac 3 phase. We already have the drive here and we read in the manual that it is not recommended to use 480 vac on a drive for a 240 vdc motor. We were going to try it anyway, thinking that it has worked for over 20 years with a Reliance drive with 480 vac, but a tech from Quantum said he did not think there was any way it could have running like that for years. Has anyone seen 240 vdc motors operate from drives with 480 vac supply voltage? Also the transformer is delta wye and the transformer has a wire going from nuetral junction on wye side, going to armature. Why would it be wired like this? Is the wire from transformer to armature to give armature ground? We are going to order a step down transformer, but I would like to learn more about this. Thanks for any information.
 
An incoming 480 VAC 3 phases DC drive can drive a 240 VDC armature motor by setting the maximum armature voltage to 240 VDC, don´t know about field voltage of the motor but you have to set the field voltage of the drive to be the same as you field motor voltage.

Anyway It´s a waste, ideally you should use a 240 VAC 3 phases in order to drive a 240 VDC motor.
 
Last edited:
Well, the problem will be that your firing angle of the SCR/IGBT will be so low that you might get poor regulation.

The field regulators of drives typically want either an isolated single phase voltage, or at a minimum, voltage really close to the rated voltage of the field, for the same reason...regulation will be better with a longer firing angle.

Your logic is interesting...why compare the performance specifications of a 20 year old drive with a new drive?

And your transformer arrangement is unusual, for sure. Sounds like they are trying to hold something to a maximum voltage, or tie the phase somehow back to the source. I'll leave it to the even older-old timers to answer this one.
 
Thanks for the replies. I was just surprised when I was told a new drive could not do what a 20 year drive has been doing. I think the Quantum guy may have thought I was lying about the 480 vac drive used with a 240 vdc armature motor. He did not think it could be done because of current peaks.
 
Rtm

I worked with a lot of old reliance drives that had a jumper selectable transformer feeding the field supply. That is where a variety of field voltages were selectable, with 500vdc being the default for a 480volt input. I believe the armature voltage was set with small pin jumpers but I am not sure how that affected the armature regulation electrically.

If I were you, I would locate a manual for your new drive and study it carefully. Often, the distributor/salesperson will not be aware of all the features it may have. The user manual should give you a definitive yes or no answer.

EDIT: How hard would it be to change the output of the secondary of your isolation transformer to 240vac? If so, will it still handle the current inrush and continuous load of the new drive?

EDIT: I have seen quite a few DC drives in which one lead from a transformer is at the same potential (same terminal block sometimes or jumpered right to it) with one of the armature leads. Can't remember the details, but I don't think its that uncommon.
 
Last edited:
I'd also double and triple check that the reliance drive was actually a nominal 500VDC drive (normal for 480VAC input now). I'm thinking you might have had a 3 pulse drive, which returned one end of the motor armature to the neutral tap on the transformer, to give cheap regen action, which would be used with a 250 VDC motor.

Running a 250VDC Motor on a 500VDC drive will result in serious (even above and beyond normal DC Machine) efficiency loss.
 
The Quantum tech is correct, you do not want to run a 240 VDC motor from a 480 volt line if the drive is a 6 pulse unit, as is the Quantum. The average DC voltage may be 240 volts but the peak voltage can be up to the peak voltage of the 480 volt line (670 volts). The commutator bar to bar voltage will be excessive and will probably cause a flash over.

Ever notice that the commutator segments are much narrower on a 500 volt motor than on a 240 volt motor. The reason is to spread the voltage over more bars between adjacent brushes, thus reducing the bar to bar voltage.

Rdrast is correct, the old drive is a 3 pulse unit. This type of drive produced half wave rectified DC. The neutral point of the wye is the return path so the drive is really operating from 480/1.73 or 277 volts, which was fine for a 240 volt motor.
 
First off it is hard to beat a Reliance drive, even the 40-50 year old VS drives.

The manual for the Quantum states Page 47 Chater 8.4:
NOTE: 240VDC MOTORS





It is recommended that when operating 240vdc motors that your 3 phase Input AC Line voltage is also 240v. We do not recommend using a 480vac drive to power a 240vdc motor. Doing so results in high motor armature current peaks which can cause excessive motor heating and possible damage. In addition, the high voltage peaks delivered by the high AC line can potentially breakdown motor insulation which can result in both motor and drive damage. If your main power is 480vac, we would recommend the use of an Isolation Step Down Transformer from 480vac to 240vac.





Personally wondering if you fully read the nameplate on the motor because I have never seen 480vac used to power 240vdc drive and motor, not without being stepped down. The Drives are usually capable of multi voltage inputs, the Quantum can go from 208 to 480, this has been standard for 40 years or more I guess.​


Motor tags the Arm V may be next to Field V and you not notice i.e. it could have been 500 Arm V 240 Field V or something along those lines and you assumed it had a 240v Armature especially if the motor nameplate is worn. I would triple check everything.​


I have not seen it done but I could see where you might be able to set one to use 277volts from 480v with Neutral. I would just do as recommended and supply it with the proper voltage.​
 

Similar Topics

Hi All, I am looking for some advice regarding the correct steps that should be taken if I was to replace an existing (but now obsolete) Third...
Replies
4
Views
2,630
I ve been trying to replace my LXm 05 drive On my project with a LXM 32 Drive. My plc is S7 300. is there anything wrong with this part of the logic.?
Replies
0
Views
690
I work for an OEM. The OEM has a test site. We wanted to test a single phase vfd. (reason, they were offered in the 1/4 hp where as the 3 phase...
Replies
8
Views
1,405
Good Afternoon , We have a number of PowerFlex 70 Drives that are on DeviceNet . These are older drives so when we replace a drive , we have...
Replies
0
Views
1,081
Good morning everyone: We had burned up Kinetix 350 drives by mistake (put AC 110V in +24V) the drive configured with existing motion group and...
Replies
5
Views
2,997
Back
Top Bottom