84 Thermocouples
bluenoser337
Apr 2003
Nova Scotia
391
There are a number of options for reading 84 thermocouples on a system I am proposing to upgrade but it can get costly and take up a lot of room. PLC platform has not been chosen yet. I have seen some info on the Red Lion CSTC8000. Has anyone used these and are there any thoughts on them, or thoughts on any other option for reading a large number of T/Cs? Momentum max 4 per card, SLC max 8, Compact max 6, Control max 8 & $$ Thanks!! đź“š
If the temperatures are not changing fast you could possibly use something like this multiplexer.
http://www.omega.com/pptst/CIO-EXP16-32.html
You will need 4 outputs to select between the 16 channels to read into 1 analog input in your PLC. Then you just keep cycling through the signals you need at the rate you want them to update. A little more work in the program but a boat load cheaper in the hardware if you wan live with only periodic updates. That will depend a lot on the process you are monitoring.
3 of the 32 point version will cover your 84 inputs.
I have used the Terminator I/O T1F-14THM from Automationdirect in the past for thermocouples. 14 inputs and the Do-more processor can be used right in the stack.
a cheap solution can be to use converters to a 4/20 mA signal, some resistors of 250 ohm and a 48 relais for each channel. this all gives one analog channel (as this is pricy.)
Good Afternoon , It seems like we always have problems with using Type J Thermocouples with our slip rings . Would using a RTD at 10...
1,641
Hi, Today I connected up a previously spare QD68TD-G module, configured for inputs from eight K-type TC's. However, when I connect a Fluke to...
23
5,500
Good Morning , We have a new packaging machine that have Slip Rings . We are using the Slip Rings for a rotary jaw assembly that has heaters...
16
5,067
Good Morning , Just wondering . I understand that millivolts change when temperature rises . Does resistance change also ? Thanks in...
2,512
We have a customer with Thermocouples and RTD's for temperature control. This temperature measurement system is not working for them as the read...
5,359