Good morning everyone:
We had burned up Kinetix 350 drives by mistake (put AC 110V in +24V)

the drive configured with existing motion group and ran fine before burned up.
At first we need to configure the same ip address for new drives by keypad input,that is only step we have to do or we have to configure it like new drive step by step followed by its manual?

Thanks!

Last edited by mike3475; May 11th, 2019 at 11:37 AM.
  Reply With Quote
Old May 11th, 2019, 02:22 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,792
Because the Kinetix 350 is a "CIP Motion" drive, all of its configuration except the IP address comes from the ControlLogix that is running it.

Set the IP address and as long as the firmware is compatible with what's in your ControlLogix project, that should be all the configuration you have to do.
  Reply With Quote
Old May 11th, 2019, 03:27 PM   #3
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 158
You are the man, Ken, appreciated your input!

Last edited by mike3475; May 11th, 2019 at 03:30 PM.
  Reply With Quote
Old May 15th, 2019, 01:51 PM   #4
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 158
today we got new Kinetix350, we only swapped memory module, then it works fine, found out this new drive with firmware reversion is 2.003, i remembered the old bad drive firmware reversion was 2.001, so that means that memory module only stores the IP address,not the firmware,right?
Thanks!
  Reply With Quote
Old May 15th, 2019, 02:37 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,792
I've used dozens of Kinetix 350 drives, but never had to think about the 2097-MEM memory module !

On the Kinetix 300 drives, that module stores all the configuration information for the drive and its indexing features.

On the Kinetix 350, I think all it stores is the IP address, and possibly the absolute position of the encoder at power-down.

It almost certainly doesn't store the drive's firmware; that's got to be in a nonremovable nonvolatile memory chip.
  Reply With Quote
Old May 15th, 2019, 06:25 PM   #6
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 158
thanks for that info!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Kinetix 350 / Ethernet/IP with a CompactLogix 1769-L18ER Baker in Virginia LIVE PLC Questions And Answers 12 March 22nd, 2019 05:50 PM
Siemens Servo motor and another brand servo Drive md.abdullah LIVE PLC Questions And Answers 8 January 12th, 2019 05:08 AM
AB Ultra Master software download OR Ultra 200 Servo Drive troubleshooting help jared_turner@brady LIVE PLC Questions And Answers 0 October 29th, 2018 05:47 PM
Select servo drive for mysterious servo motor HJTRBO LIVE PLC Questions And Answers 11 August 12th, 2014 06:00 PM
Servo drive failures rsdoran LIVE PLC Questions And Answers 17 May 5th, 2004 11:06 PM


All times are GMT -5. The time now is 02:37 PM.


.