how to monitor a pulse

I have an oiler that needs to be monitored. The oiler lubes a head bearing at a rate of 9 pulses a minute. If the pulses fall to 7 pulses/min or go over 11 pulses/min the head motor needs to shut down or start an alarm.

Oiler pulses are 24V DC

This is the way I am currently thinking. Covert the pulses to RPM and use a limit function block for the high and low limits. I don't know if this is possible and looking for input.

PLC= Modicon M340
Software=Unity Pro
Progamming Language=Ladder
PLC expertise=beginner
  Reply With Quote
Old May 13th, 2019, 07:51 PM   #2
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,374
HI and Welcome to the Forum.
Quote:
This is the way I am currently thinking. Covert the pulses to RPM and use a limit function block for the high and low limits.
That isn't a bad idea.

How are you getting that "pulse"? From a mag switch? Cam Switch or ?? Depending on the switch and how it works you may need to put in some "debounce" timers into your program to keep from measuring more than one pulse every time.

Is the pulse rate constant? In other words do you get pulses every X seconds?

How long can the head turn with no pulses? How long can you go if there are too many pulses?

These are all things you will want to keep in mind when you design your program. You want to protect the equipment but at the same time keep nuisance alarms from happening. It is my experience that if you keep your shut downs too tight eventually they find a way to override the shutdown and that is when bad things happen.

Good luck and check back if you need more help.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old May 13th, 2019, 07:57 PM   #3
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 315
Why not just set and reset two timers every other pulse? One is timing or the other is...,If one times out, Bingo!
  Reply With Quote
Old May 13th, 2019, 08:02 PM   #4
kevoler
Member
Canada

kevoler is offline
 
Join Date: May 2019
Location: Canyon
Posts: 2
Hi Bullzi,

[Good luck and check back if you need more help.]
I do need more help as I am new to plc programming I need some examples in Ladder on how to implement my plan.
  Reply With Quote
Old May 13th, 2019, 08:17 PM   #5
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,771
How quickly do you need to react?
The quickest reaction would be to set up a timer that runs continuously and resets at each oiler pulse. If the timer's accumulated value is less than 5.45 seconds when you sense the oiler pulse, that's a rate greater than 11 pulses per minute. If the timer's accumulated value is greater than 8.6 seconds when you sense the oiler pulse, that's a rate less than 7 pulses per minute.
If you can wait up to a full minute before you react you could set up a counter to keep track of each pulse and reset it once per minute. If the count is over 11 or under 7 when it comes time to reset, you sound the alarm.
  Reply With Quote
Old May 14th, 2019, 09:09 AM   #6
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,143
I'd read the "pulses" as digital inputs tied to a counter, and have a timer running set to 1 minute. You could then use two rungs, each with a comparison FB, one if the counter's accumulator is below 8 and the other if the accumulator is above 10. The timer's done bit would be at the beginning of each rung and a discrete bit would be at the end. When the timer goes done if the counter is less than 8 or more than 10 then that rung would be true enabling it's bit. If neither bit is enabled then the timer and counter simply reset. If either one of the bits is enabled then you set the alarm.
__________________
Go Hawks!!!
  Reply With Quote
Old May 14th, 2019, 01:47 PM   #7
STEMAPPLICATIONS
Member
Canada

STEMAPPLICATIONS is offline
 
STEMAPPLICATIONS's Avatar
 
Join Date: Sep 2008
Location: Alberta
Posts: 16
Usually the way I've seen it done and IMHO the most effective is to have a sensor on each line from the manifold to the machine. There are so many ways to sense pulsing that I won't even get into it but the basics are to have a discrete sensing device that has the pressure differential that you desire for low and high. Your pump is on a timer to deliver X volume of lubricant. Your high timer runs once the pump comes on and you have so many seconds to see the pulse from the line come on. If the timer times out, declare a leak. Your low timer runs once the pump is running AND a high pulse is detected and you have so many seconds to see it fall. If the timer times out declare a blockage. If the high timer triggers an alarm, the low timer alarm is over-ridden. So you need to know what the pressure rise and fall time is typical by observation of a properly running system. A good machine millwright/mechanic is your best partner to determine that.

That's the way I have either seen it done or corrected systems to do so.

Last edited by STEMAPPLICATIONS; May 14th, 2019 at 01:58 PM.
  Reply With Quote
Old May 14th, 2019, 04:50 PM   #8
wancues
Member
United States

wancues is offline
 
wancues's Avatar
 
Join Date: Nov 2012
Location: moxee
Posts: 45
i do the same as firejo. count pulses. when time expires i use lim to check count
__________________
John

To error is human to really foul things up requires a computer
  Reply With Quote
Old May 15th, 2019, 02:53 PM   #9
JGax
Member
Mexico

JGax is offline
 
Join Date: Nov 2013
Location: Mexicali
Posts: 23
Quote:
Originally Posted by kevoler View Post
I have an oiler that needs to be monitored. The oiler lubes a head bearing at a rate of 9 pulses a minute. If the pulses fall to 7 pulses/min or go over 11 pulses/min the head motor needs to shut down or start an alarm.

Oiler pulses are 24V DC

This is the way I am currently thinking. Covert the pulses to RPM and use a limit function block for the high and low limits. I don't know if this is possible and looking for input.

PLC= Modicon M340
Software=Unity Pro
Progamming Language=Ladder
PLC expertise=beginner
I think your idea is great....
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Pulse Width Modulation for CL2 dosing; nearly figured out, just need a little help defcon.klaxon LIVE PLC Questions And Answers 6 June 27th, 2018 09:33 PM
Foxboro CFT50 pulse output 95ee32069 LIVE PLC Questions And Answers 0 January 6th, 2011 01:24 PM
Pulse Count - not exactly what flowmeter says it should be (Logix 500) TimD LIVE PLC Questions And Answers 9 October 2nd, 2007 09:55 PM
s7-200 High Speed Pulse Output / Counter hawkeyen2001 LIVE PLC Questions And Answers 0 September 19th, 2007 07:28 AM
Count the length of Pulse signal Steve Cheung LIVE PLC Questions And Answers 7 November 21st, 2004 12:45 PM


All times are GMT -5. The time now is 05:57 AM.


.