Hi, I am attempting to setup some PF700VC's on 20-comm-e's on an ethernet network and i have run into some wierdness.
basically the setup is as follows
Control Logix L61 rev'd up to V17 so it can see the V7.01 PF700's
standalone ethernet network with stratix 8000 switch.
6x PF 700VC V7.01 with 20-comm-e
I have added the drives to the product tree in the CLX program and they are happily appearing in there, product keying is turned on and all is good there. the data tables have been created automatically.
everything went super smooth there (once i flashed up to V17 as V16 didnt support the version number of the PF700VC's)
i have set speed reference to DPI 5
I cannot get the drive to respond to SOME of the output commands in the CLX databables
now using drive executive I can see the following.
CLX Datatable PF700 Control bits.
stop stop bit changes state (drive flashes orange - stop asserted)
start bit no effect
job bit no effect
speedredD1 set to 0 in plc is set to 1 in the VSD (preset speed 2???)
speedrefD2 set to 0 in plc is set to 0 in the VSD
speedrefD3 set to 0 in plc is set to 0 in the VSD
commanded speed (varies) i can see this appearing in the commanded speed in the vsd but is not being passed
onto the speedref. using hte flow chart in drive explorer i cannot see why as as appears ok
so basically i defiantly have comms although the things that can cause motion are not working?????????????
help? im really stuck for ideas
p.s. screen dump attached, please note only 2 VSD's are connected at this time...
should i just ditch this and go with a message???
basically the setup is as follows
Control Logix L61 rev'd up to V17 so it can see the V7.01 PF700's
standalone ethernet network with stratix 8000 switch.
6x PF 700VC V7.01 with 20-comm-e
I have added the drives to the product tree in the CLX program and they are happily appearing in there, product keying is turned on and all is good there. the data tables have been created automatically.
everything went super smooth there (once i flashed up to V17 as V16 didnt support the version number of the PF700VC's)
i have set speed reference to DPI 5
I cannot get the drive to respond to SOME of the output commands in the CLX databables
now using drive executive I can see the following.
CLX Datatable PF700 Control bits.
stop stop bit changes state (drive flashes orange - stop asserted)
start bit no effect
job bit no effect
speedredD1 set to 0 in plc is set to 1 in the VSD (preset speed 2???)
speedrefD2 set to 0 in plc is set to 0 in the VSD
speedrefD3 set to 0 in plc is set to 0 in the VSD
commanded speed (varies) i can see this appearing in the commanded speed in the vsd but is not being passed
onto the speedref. using hte flow chart in drive explorer i cannot see why as as appears ok
so basically i defiantly have comms although the things that can cause motion are not working?????????????
help? im really stuck for ideas
p.s. screen dump attached, please note only 2 VSD's are connected at this time...
should i just ditch this and go with a message???