So, I am covering for a colleague who is out this week, and I started to check out a control panel he had designed. To my surprise, I opened the door, and every single wire inside was grey!
Apparently, the customer this panel is built for has a spec for 7-stranded wire with a specific insulation. It sounds like all they could get (in a timely manner, not ALL they could get) was that specific wire in grey. The customer approved said panel change.
I popped open my NFPA 79 code and stared looking through the conductor sections. (see code excerpts below)
So, the first two paragraphs concerning the grounded conductor and interlocks both use the terminology “SHALL” which leads me to think there is NO interpretation. It sounds like the control circuit and power wiring could technically be gray? I’m not even sure what would be posted on the inside of the cabinet – all of the wire numbers and their voltages?
Is this panel a code violation? Personally, if I were working on this panel in the field, I would look at the panel and just say No Thanks, next please. Maybe there are industries that use all one color?
Code excerpts:
Section 13.2.3.1 Uses the terminology “..this conductor shall be WHITE, GRAY, or three continuous WHITE stripes on other than GREEN, BLUE, or ORANGE insulation along its entire length”
Section 13.2.4.1 “The color ORANGE shall be used to identify ungrounded conductors that remain energized when the main supply circuit disconnecting means is in the off position. This color identification shall be strictly reserved for this application only
Section 13.2.3.4 “Where color coding is used for identification of conductors, the following color codes shall be permitted to be used:
1. BLACK for ungrounded AC and DC power conductors
2. RED for ungrounded AC control conductors
3. BLUE for ungrounded DC control conductors
Where the identification is other than as permitted in 13.2.3.4, the means of identification shall be permanently posted on the inside of the main electrical control panel enclosure in a visible location.
Apparently, the customer this panel is built for has a spec for 7-stranded wire with a specific insulation. It sounds like all they could get (in a timely manner, not ALL they could get) was that specific wire in grey. The customer approved said panel change.
I popped open my NFPA 79 code and stared looking through the conductor sections. (see code excerpts below)
So, the first two paragraphs concerning the grounded conductor and interlocks both use the terminology “SHALL” which leads me to think there is NO interpretation. It sounds like the control circuit and power wiring could technically be gray? I’m not even sure what would be posted on the inside of the cabinet – all of the wire numbers and their voltages?
Is this panel a code violation? Personally, if I were working on this panel in the field, I would look at the panel and just say No Thanks, next please. Maybe there are industries that use all one color?
Code excerpts:
Section 13.2.3.1 Uses the terminology “..this conductor shall be WHITE, GRAY, or three continuous WHITE stripes on other than GREEN, BLUE, or ORANGE insulation along its entire length”
Section 13.2.4.1 “The color ORANGE shall be used to identify ungrounded conductors that remain energized when the main supply circuit disconnecting means is in the off position. This color identification shall be strictly reserved for this application only
Section 13.2.3.4 “Where color coding is used for identification of conductors, the following color codes shall be permitted to be used:
1. BLACK for ungrounded AC and DC power conductors
2. RED for ungrounded AC control conductors
3. BLUE for ungrounded DC control conductors
Where the identification is other than as permitted in 13.2.3.4, the means of identification shall be permanently posted on the inside of the main electrical control panel enclosure in a visible location.