Logix 5000 - Cascade Loop+ Feedforward problem on loop activation

harryting

Lifetime Supporting Member
Join Date
May 2002
Location
Puget Sound
Posts
2,595
Just to check my sanity even though I think I found the solution.

So, for this loop with long lag time we got 2 PID loops with the Outer Loop setting the setpoint for the inner loop in a 5380 processor. We used the standard PID ladder instruction and things looks good. The inner loop gets the outer loop setpoint.

We also have a feedforward component that feed into the .BIAS of the outer loop.. Again, it seems to work and we can see the CV change when the feedfoward changes.

However...

One problem that showed up is that on the activation of the loop. The output doesn't reflect the Feedfoward at all so with the slow tuning the output stays at 0 for long time. I think this is just how it works but I want to check with yall to make sure that I'm not missing anything. I can remedy this problem by jamming the FF into the output of the PID upon activation but wonder if there's more elegant or recommended way to do this.
 
Does the outer loop have integral action, or P-only? If P-only, there is a .NOBC bit that will affect the .BIAS term at the manual-to-auto transition.
 

Similar Topics

Hi all, Having some issues setting up a PIDE Cascade control loop. Have been trying to go through the Wp008 doc but there's probably something...
Replies
9
Views
5,611
Hi there, I need to wite the logic to control a cascaded PID loop with the following characteristica: 1- Master : Density 2- Slave : Water...
Replies
5
Views
12,839
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
146
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
571
Back
Top Bottom