I have an analog input that is used as the PV to a PID.
The PID controls an analog out.
The analog out is connected to a transducer.
The PID is reading the input at just above zero and has ramped up the output to 100% .
The transducer does not respond. (the whole loop worked perfectly Friday. I do not think I made any changes today that would affect this loop.
The analog output connected to the analog out is supplying 4.8mA DC as indicated by a FLuke DMM in series with the output.
I don't see how this is possible unless the analog out malfunctioned over the weekend while it was off.
I will switch to the other analog out as a test.
As confirmation , the gauges and general obsevation agree that the output is not on.
The PID controls an analog out.
The analog out is connected to a transducer.
The PID is reading the input at just above zero and has ramped up the output to 100% .
The transducer does not respond. (the whole loop worked perfectly Friday. I do not think I made any changes today that would affect this loop.
The analog output connected to the analog out is supplying 4.8mA DC as indicated by a FLuke DMM in series with the output.
I don't see how this is possible unless the analog out malfunctioned over the weekend while it was off.
I will switch to the other analog out as a test.
As confirmation , the gauges and general obsevation agree that the output is not on.