plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old June 30th, 2020, 12:57 PM   #1
phuz
United States
phuz is offline
Scaling changes with 1794-IT8 over Ethernet to L81
Just commissioned two new skids for a customer. Each has a 1794 chassis over Ethernet back to an L81. The second module of each chassis is a 1794-IT8 and each has 3 Type J thermocouples. The temperatures we are measuring are around 30C, so the raw input from the module normally shows 300. What has happened now is that these readings will increase by a factor of 10 to ~3000. This occurs on all three thermocouples on both 1794-IT6 modules. The TCs are Type J and the module is set for Type J. Not much configuration in these, so what could possibly cause the resolution to increase that much? CJCs are installed. TB3T bases are used.
Old June 30th, 2020, 01:27 PM   #2
id10t_error
United States
id10t_error is offline
id10t_error's Avatar
What do you have selected for the data format?
__________________
"We make the solutions up out of modules, so they're all standard, ... They're built for security, reliability, ease of expansion and ease of changing. They're the ideas we had many years ago that tend to get lost today." -Ken Olsen co-founded Digital Equipment Corporation (DEC)
Old June 30th, 2020, 01:33 PM   #3
phuz
United States
phuz is offline
Quote:
set to C
Old June 30th, 2020, 01:38 PM   #4
phuz
United States
phuz is offline
I just noticed that each module does have a CJC fault, but they appear to be connected per the manual.
Old July 1st, 2020, 05:36 PM   #5
phuz
United States
phuz is offline
Update:
When using grounded TCs, terminal #16 needs to be tied to ground.
Our issue has been resolved.
Old July 1st, 2020, 07:31 PM   #6
Mickey
United States
Mickey is offline
Mickey's Avatar
Quote:
Originally Posted by phuz View Post
Update:
What terminal base are you using?
Isn't #16 the 24v dc common to power the base and module power.
Can you point to this tidbit of info.
Don't like grounded TC's. Ground loops and noise problems. see pdf
https://blog.wika.us/products/temper...vs-ungrounded/
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old July 1st, 2020, 10:02 PM   #7
phuz
United States
phuz is offline
TB3T base.
I think it is, but apparently this was a Rockwell secret for grounded TCs.
Old July 2nd, 2020, 12:29 AM   #8
Mickey
United States
Mickey is offline
Mickey's Avatar
TB3T base.
HMMM? Whatever works.
__________________
Mickey
Old July 2nd, 2020, 06:25 AM   #9
phuz
United States
phuz is offline
Quote:
Exactly! I saw no reference to this in the manual, but this came from a second call to Rockwell and apparently is one of their undocumented notes.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
OMRON CJ1's Ethernet Networking problems castro LIVE PLC Questions And Answers 6 June 8th, 2009 06:57 AM
PlC5 Ethernet, a warning, a story, and a question allscott LIVE PLC Questions And Answers 5 December 8th, 2006 01:05 PM
Using a RADES9300 and serial ethernet to connect to plc...Works over eth but not dial bdoub1eu LIVE PLC Questions And Answers 5 July 28th, 2006 09:30 PM
AB Softlogix Version 13 and MSG over Ethernet Roy C. LIVE PLC Questions And Answers 0 October 19th, 2004 07:41 PM
Profi-bus or Ethernet Shailesh10 LIVE PLC Questions And Answers 1 December 31st, 2003 02:19 AM