Old June 30th, 2020, 08:51 AM   #31
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is online now
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 6,934
Quote:
Originally Posted by akky View Post
if suppose this is the case, is there a way to reverse it or change it in anyway?

will serial communication work?
Yes your serial connection should still work, you will need a 1761-CBL-PM02 cable then you can change the Ethernet settings
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old June 30th, 2020, 09:19 AM   #32
akky
Member
India

akky is offline
 
Join Date: Apr 2020
Location: Mumbai
Posts: 13
Quote:
Originally Posted by geniusintraining View Post
Yes your serial connection should still work, you will need a 1761-CBL-PM02 cable then you can change the Ethernet settings
Yes I have the cable.. Ill check it in a few days and give an update on the same.
But can you tell me which driver to select?
  Reply With Quote
Old June 30th, 2020, 09:22 AM   #33
alan_505
Member
Australia

alan_505 is offline
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 627
RS232 DF1
then set the com port to what your USB to serial adapter is using or if you have a real serial port set it to that COM address (usually COM1)
once you have set the correct COM you should be able to click on autobrowse and it should find the correct settings for the ML1400's serial port.

Alan.
  Reply With Quote
Old June 30th, 2020, 09:25 AM   #34
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is online now
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 6,934
Like Alan said the DF1

Here is a video that may help, I am using a USB cable so if you are not then select COM1

http://www.youtube.com/watch?v=QIu1AGUR4N8
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old July 1st, 2020, 12:42 AM   #35
akky
Member
India

akky is offline
 
Join Date: Apr 2020
Location: Mumbai
Posts: 13
Quote:
Originally Posted by geniusintraining View Post
Yes your serial connection should still work, you will need a 1761-CBL-PM02 cable then you can change the Ethernet settings
Hi,
So actually i have the AB 1763-NC01 cable and not the one you mentioned. So is there any way this would work through RS-485 mode of communication?
I have a USB to RS-485 converter with me.
  Reply With Quote
Old July 1st, 2020, 06:14 AM   #36
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is online now
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 6,934
I have never tried, your PLC would need to be setup for 485 first and I think you would need to download that to the processor....

There is a chance that you could use the NC01 to make a PM02, you would need to verify the pinout of the two and compare them, the NC01 is not a converter its only connects to the pin so in theory its RS232 and could work as a PM02 if the pins are correct

I know Mickey has posted the pinout of the of the NC01 before
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old July 1st, 2020, 01:33 PM   #37
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,357
Here..
Attached Files
File Type: doc 1763_NC01_cable_pin_out__Answer_ID_34450.doc (26.0 KB, 2 views)
File Type: pdf 1761-CBL-PM02-PinOut.pdf (21.3 KB, 3 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old July 2nd, 2020, 03:01 AM   #38
akky
Member
India

akky is offline
 
Join Date: Apr 2020
Location: Mumbai
Posts: 13
Quote:
Originally Posted by Mickey View Post
Here..
ok Mickey thanks, ill check on this and update in some days.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Micrologix question Holly LIVE PLC Questions And Answers 20 October 12th, 2019 01:53 PM
Hi I want to use Flex I/O ethernet IP 1794 AENT with Micrologix 1400 psaundary LIVE PLC Questions And Answers 5 August 20th, 2015 07:45 AM
micrologix 1400 configuration with rslogix 500 sruthi LIVE PLC Questions And Answers 4 April 7th, 2014 07:50 PM
Drive ethernet lost communication (micrologix 1400/ panel view) jimbob187jim LIVE PLC Questions And Answers 1 July 31st, 2013 11:41 AM
MicroLogix 1400 Network seaston_65 LIVE PLC Questions And Answers 2 July 15th, 2011 01:57 PM


All times are GMT -4. The time now is 12:11 PM.


.