Transfer Analog signals from remote I/O to DCS

I would like to enquire for a product as a solution for our on-going project.

We need to transfer some analogue signals (QTY:08 / 4-20mA ) from Remote I/O cabinet to our DCS System (Hardwired).

We have signals in an output (4-20 mA) form and now we are looking for a multiplexer and Demux system to transfer data using twisted pair.

The length between Point A to Point B is almost 1.5 KM.

As requested by customer, we canít offer them any wireless solution. Can you kindly recommend us which multiplexer system can be used in this situation to transfer noise free data.

Your immediate reply will be highly appreciated.
  Reply With Quote
Old June 29th, 2020, 11:15 AM   #2
Vlad Romanov
Member
United States

Vlad Romanov is offline
 
Join Date: Sep 2017
Location: Los Angeles
Posts: 176
I'm not fully understanding what you're trying to do with the signals, but a common approach is to have a remote analog input card in the field that would receive the signals, digitize them and send over EtherNet, DeviceNet, PROFIBUS, etc.

If I was given the information above, I would utilize PointIO from Rockwell and read the signals over EtherNet (however you want to bring it over; I'm thinking fiber optic would be needed for such distance).

Cheers,
Vlad
__________________
PLC Technical Tutorials & Courses SolisPLC PLC Programming
  Reply With Quote
Old June 29th, 2020, 11:30 AM   #3
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,527
I would agree with Vlad. The network cable should be long, not the signal wires.


If you're using Remote IO, it is usually placed near to the IO. You can then do your communication via fiber optic Ethernet, over some IO network (Profinet, EthernetIP, ModbusTCP, etc), or a fieldbus that supports fiber.
  Reply With Quote
Old June 29th, 2020, 11:52 AM   #4
exabmorgan
Member
United States

exabmorgan is offline
 
Join Date: Feb 2008
Location: USA
Posts: 70
I've used these:
https://www.netsys-direct.com/collec...r-nv-202rpekit

Then whatever ethernet based remote IO
  Reply With Quote
Old June 30th, 2020, 08:13 AM   #5
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 260
For that kind of distance I would recommend you use Profibus PA, which can power the devices. You need a plc with analog output cards to connect to the DCS. Then the pkc needs a Profibus DP or Profinet scanner. It be required either a DP/PA converter or Profinet/PA gateway. Profibus PA is slow, only 31.25 kbaud, but normally this is OK on many process applications. A bit of logic that reads the PA inputs and maps them to the analog output of the PLC should be good for this solution.
  Reply With Quote
Old June 30th, 2020, 01:55 PM   #6
K.Anwar
Member
Saudi Arabia

K.Anwar is offline
 
Join Date: Jun 2020
Location: Khobar
Posts: 4
Hello Everyone!

Thanks all for your immediate responses.

The Scenario is ; Client is saying me to fetch data from a remote I/O cabinet having Siemens remote Analog output module.

He will configure the 4-20 mA signals to that RIO Cabinet (Having an analog output Card). This means from there, I am required to take that signal to my PLC station(Siemens Analog input cards) as hardwired (Distance is about 1.5 Km). As the distance is too much i can not use multi-core hardwired cable.

I searched on Internet there is a multiplexer system which take 4-8 analog input signals, transfer that to a twisted pair FO cable and on the other end we can use a demultiplexer to get those 4-8 Analog signals. Does any one know about this multiplexer and demultiplexer system? Or any other solution so that i can transfer those signals without any signal data losses.

Immediate response will highly be apreciated
  Reply With Quote
Old June 30th, 2020, 02:08 PM   #7
K.Anwar
Member
Saudi Arabia

K.Anwar is offline
 
Join Date: Jun 2020
Location: Khobar
Posts: 4
Quote:
Originally Posted by Vlad Romanov View Post
I'm not fully understanding what you're trying to do with the signals, but a common approach is to have a remote analog input card in the field that would receive the signals, digitize them and send over EtherNet, DeviceNet, PROFIBUS, etc.

If I was given the information above, I would utilize PointIO from Rockwell and read the signals over EtherNet (however you want to bring it over; I'm thinking fiber optic would be needed for such distance).

Cheers,
Vlad
Thanks for your response; what I want is to take those analogue output signals (from Siemens Analog output card at field) and communicate it with my SCADA (Spare Siemens Analog input cards are present). So in overall , just to take that output signals and configure those in my analogue input Card. Issue: The distance is 1.5 Km and signal will be lost if take signals as hardwired.
  Reply With Quote
Old June 30th, 2020, 03:03 PM   #8
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,527
Quote:
Originally Posted by K.Anwar View Post
The Scenario is ; Client is saying me to fetch data from a remote I/O cabinet having Siemens remote Analog output module.

I'm going to be frank, as far as I'm concerned, your client is asking you to do something dumb. I guess I could be wrong.



You'll probably spend enough money to buy & troubleshoot the HW multiplexer system, that it would just make sense to put a remote IO rack in their panel, and run the remote IO back over the FO cable instead as Profinet (or Profibus, if you must). The actual Hard Wired part would only be a few feet long, and the rest is a robust and practically noise proof Ethernet solution.



Another potential option would be to use some kind of gateway (PN/PN coupler, anybus, whatever) to send IO data directly from one PLC to the other, without messing about with hardwiring IO signals.
  Reply With Quote
Old June 30th, 2020, 06:51 PM   #9
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 260
MK42, I agree with your solution. I misunderstood the original explanation
  Reply With Quote
Old July 1st, 2020, 09:04 AM   #10
K.Anwar
Member
Saudi Arabia

K.Anwar is offline
 
Join Date: Jun 2020
Location: Khobar
Posts: 4
Quote:
Originally Posted by mk42 View Post
I'm going to be frank, as far as I'm concerned, your client is asking you to do something dumb. I guess I could be wrong.



You'll probably spend enough money to buy & troubleshoot the HW multiplexer system, that it would just make sense to put a remote IO rack in their panel, and run the remote IO back over the FO cable instead as Profinet (or Profibus, if you must). The actual Hard Wired part would only be a few feet long, and the rest is a robust and practically noise proof Ethernet solution.



Another potential option would be to use some kind of gateway (PN/PN coupler, anybus, whatever) to send IO data directly from one PLC to the other, without messing about with hardwiring IO signals.
Dear mk,

That could be a dumb thing for us but as you know, we can only propose them a solution. Actually, There are two Separate plants that's why client doesn't want us to give any accessibility to one another (Any CPU to CPU connectivity over same ethernet network). This is the reason he is saying that he will generate output from his side and then we may fetch data to our PLC. So there will be no connectivity between two PLCs but we will have data on our side.

it would be a great help if you have any idea about peer-to-peer communication? kindly look below the attachment, this is the solution i want.

PeertoPeer.JPG
  Reply With Quote
Old July 1st, 2020, 10:12 AM   #11
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,527
Quote:
Originally Posted by K.Anwar View Post
So there will be no connectivity between two PLCs but we will have data on our side.

it would be a great help if you have any idea about peer-to-peer communication?

Remote IO hard wired into their IO would provide no connectivity between the two CPUs, so it could qualify. However, you would have a network connection from one plant to the other, even if it didn't allow communication between the PLCs, which is probably the real concern.



A Peer to peer solution could potentially work. The picture you put in seems promising, but I don't know what product that is to know further. I've never used something like that.
  Reply With Quote
Old July 2nd, 2020, 03:00 AM   #12
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 1,646
Phoenix also makes something that may be usable...

https://www.phoenixcontact.com/onlin...8-47e86495ed41

I've used something similar (although it would have been much higher bandwidth) and the cables must be really good and not jump through junction boxes, etc... The distance was about 800 meters and it wouldn't work, but these were 40 to 50 year old cables with a few junction boxes in between so it didn't surprise me in the end.

What PLC's are being used here? Can you install a junction box with power at about halfway between both of the PLC's? If they're both Siemens, I was thinking that you could install a profibus link and stick a DP coupler in the middle which doesn't let one company access to the other side. Another option could be to set up two gateways which will too insulate the two networks whilst being slightly easier to do than wire signals.

And the reason I mention this is that I can almost guarantee you that two months after you've completed the hard wiring, someone is going to come back to you and ask for an awful lot more signals.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
MLX 1400 with POINT I/O JeffKiper LIVE PLC Questions And Answers 23 June 18th, 2014 12:39 AM
Difference between Local I/O and Remote I/O obi1987 LIVE PLC Questions And Answers 3 May 17th, 2014 06:20 AM
Analog data coming from DCS fluctuaing jainil2210 LIVE PLC Questions And Answers 7 April 24th, 2014 08:42 PM
Analog I/O in AllenBradley PLC5 Frelecing LIVE PLC Questions And Answers 9 October 18th, 2010 02:16 PM
Economical Remote I/O zmanvortex LIVE PLC Questions And Answers 19 February 17th, 2006 05:01 PM


All times are GMT -4. The time now is 08:25 AM.


.