Old June 30th, 2020, 04:51 PM   #16
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
As requested. The runtime looks different due to me adding them manually as suggested by Rockwell Technical Support.
Attached Images
File Type: png Design.PNG (50.0 KB, 15 views)
File Type: png shortcut verifier.PNG (50.4 KB, 15 views)
File Type: png Runtime.PNG (30.0 KB, 12 views)
  Reply With Quote
Old June 30th, 2020, 05:21 PM   #17
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 258
When you put the non working version in the HMi, can you ping it from your network with your PC?

Are you keeping the frimware the same or changing it each time you revert back? I don’t believe a firmware change Will wipe the IP address on the hmi, but it is Rockwell, anything is possible.

Sometimes it’s the easy things. Maybe try to see it in linx as well?
  Reply With Quote
Old June 30th, 2020, 05:23 PM   #18
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
I can see the processor, I can ping it and I can see the HMI establish two CIP connections to the processor.
  Reply With Quote
Old June 30th, 2020, 05:41 PM   #19
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 258
Are you using the ME transfer utility? If so do you have “replace communications” checkbox selected when doing the transfer?
  Reply With Quote
Old June 30th, 2020, 06:24 PM   #20
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
Quote:
Originally Posted by _Dock_ View Post
Are you using the ME transfer utility? If so do you have “replace communications” checkbox selected when doing the transfer?
yes
  Reply With Quote
Old June 30th, 2020, 09:12 PM   #21
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 258
Well, all the basics seem to be covered. You are concerned with the node limit. If possible have you tried removing a few devices to see if the problem resolves itself? The only clear path of consistency I can see is that your colleagues have the same issue, that would say hardware issue to me.

I’m sure you’ve considered these things. I just don’t know what else to offer you to help. If not a hardware problem, then this is deep in software somewhere that is probably a perfect storm to your application.

Judging by the lack of responses by people on this website that are way smarter than me I would guess they are stumped as well.
  Reply With Quote
Old June 30th, 2020, 09:14 PM   #22
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 258
With the new revamp to the knowledge base it is mostly useless. I looked through some of the articles and nothing seemed to apply to your problem.
  Reply With Quote
Old June 30th, 2020, 09:20 PM   #23
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
Quote:
Originally Posted by _Dock_ View Post
With the new revamp to the knowledge base it is mostly useless. I looked through some of the articles and nothing seemed to apply to your problem.
Agreed. I gave up on it for the day. I have made sure I was down to 28 CIP connections out of 32 being used when I put the rev 10 HMI in place. Still, no luck.
  Reply With Quote
Old July 1st, 2020, 07:44 AM   #24
Jmeadows7676
Member
United States

Jmeadows7676 is offline
 
Join Date: Oct 2013
Location: Alabama
Posts: 75
You could make a test project just to see where the problem is. Create a New Project talking to those PLCs if it works then something is up with the Conversion from 6 to 10.
  Reply With Quote
Old July 1st, 2020, 08:30 AM   #25
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
Quote:
Originally Posted by Jmeadows7676 View Post
You could make a test project just to see where the problem is. Create a New Project talking to those PLCs if it works then something is up with the Conversion from 6 to 10.
I will try that today. Thanks.
  Reply With Quote
Old July 1st, 2020, 09:47 AM   #26
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,885
The Communications Setup can contain devices that no longer exist. As you connect to networks it will discover devices. Then if you connect on a different network those devices are "hidden". So it maintains a sort of history of devices. On the Ethernet driver there is an option to Show All Devices. Deleting shortcuts does not delete this "history".

What I would try next, is to delete the RSLinx Enterprise (or the new name: FactoryTalk Link) server and then recreate it. Then recreate the shortcuts. This will wipe out all of the old stuff.

On another note, the Shortcut Verify button is useless. It does not verify the shortcut at all. It simply verifies that you have selected a device on the Local and the Runtime tabs, as well as checking for an offline tag file. It does not verify that the shortcut actually works.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old July 1st, 2020, 09:57 AM   #27
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
Quote:
Originally Posted by Operaghost View Post
The Communications Setup can contain devices that no longer exist. As you connect to networks it will discover devices. Then if you connect on a different network those devices are "hidden". So it maintains a sort of history of devices. On the Ethernet driver there is an option to Show All Devices. Deleting shortcuts does not delete this "history".

What I would try next, is to delete the RSLinx Enterprise (or the new name: FactoryTalk Link) server and then recreate it. Then recreate the shortcuts. This will wipe out all of the old stuff.

On another note, the Shortcut Verify button is useless. It does not verify the shortcut at all. It simply verifies that you have selected a device on the Local and the Runtime tabs, as well as checking for an offline tag file. It does not verify that the shortcut actually works.

OG

I did that under the runtime tab. I deleted all of the devices under the backplane as suggested by Rockwell Technical Support. It did not work.
  Reply With Quote
Old July 1st, 2020, 10:13 AM   #28
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,885
No, I am saying to delete the server. Not the shortcuts or the hidden devices. Make it rebuild the comms server.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old July 1st, 2020, 10:44 AM   #29
Kroger2013
Member
United States

Kroger2013 is offline
 
Join Date: Dec 2013
Location: USA
Posts: 32
Quote:
Originally Posted by Operaghost View Post
No, I am saying to delete the server. Not the shortcuts or the hidden devices. Make it rebuild the comms server.

OG
Are you talking about deleting the server under the Communications tab?
  Reply With Quote
Old July 1st, 2020, 11:38 AM   #30
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,885
Right-click on RSLinx Enterprise/FactoryTalk Linx and delete it. You can add it back in the same way.

I would delete it and probably reboot the PC before I added it back.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
FTView ME Station Tags Issue Bbarnett LIVE PLC Questions And Answers 2 August 1st, 2019 02:15 PM
Studio 5000 v27 windows 10 J2009 LIVE PLC Questions And Answers 19 February 28th, 2019 01:47 PM
L35E Serial Comm OK, Processor Not Showing karlsigl LIVE PLC Questions And Answers 29 November 8th, 2014 05:59 AM
Disappearing Trigger Labels - FTView Studio JonHopper LIVE PLC Questions And Answers 0 October 29th, 2014 11:54 AM
Ton Timer ICAPALDO LIVE PLC Questions And Answers 41 December 21st, 2004 05:43 PM


All times are GMT -4. The time now is 08:35 AM.


.