Hi

On the firmware upgrade side of these little beasts

Do you have to pay every time you do the firmware ug ?

I looked in the manual and it gives part numbers with licenses for

1,5,10, 25 etc upgrade licenses ?

Also whats the difference between the two media kits ?

A little confused!

Oh and btw the panelview plus is one i am getting to play with its an

HMI 2711P-RDT10C Screen Only so ill obviosly need to order a logic module but will i need the comms module if i use etherent ?
Its a Series A Rev. B.
 
No. The only upgrade I think you have to pay for is the one the involves going from 3.0 to 3.1. In that case the WinCE OS is the first step the upgrade process, going from Win3.0 to Win4.0. It is for this upgrade that MicroSoft compells Rockwell to charge a licencing fee. An unfortunate gotcha that Rockwell does not intend to get caught with again.

If you ask your distributor nicely, or make enough squeal, they will often come to the party.

If you are just using the Ethernet port, which is what I would normally recomend, then it is not necessary to use any piggyback comms modules.
 
The 7" and larger PV+ terminals use the same logic module, which includes an Ethernet port.

Any series and revision of display module is going to be compatible with any revision of logic module. There's a compatibility rule with the internal CompactFlash cards, for some reason, but that's always included with a Logic module.

Be sure not to try to cross a PV+ display module with a VersaView CE logic module; the two types are keyed (for reasons I will never understand) so they will warn you at every bootup if you have parts from two different terminals.

Again, the firmware upgrade was only 3.0 -> 3.1, and every distributor in the world still has some license kits around leftover from the Great Migration.
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
70
Hi everyone, I've been tasked with creating a basic HMI for commissioning purposes for two pumps on a AB Panelview Plus 1000, 2711PRDT10C. I have...
Replies
16
Views
2,744
im tring to find out if i have a bad power supply for my panelview 1000 plus. does anyone have the pinout for the 10 pin connector on the...
Replies
1
Views
1,833
I need an X/Y plot to visually represent data o a roundness gage I am designing. ActiveX ME Chart Control UDT seems broke. Any advise one how to...
Replies
0
Views
649
Hello Everyone, I hope we are all good today! I have a project from 2015, and the customer is locked out of the HMI. They do not know what the...
Replies
5
Views
1,934
Back
Top Bottom