CP 5711 9-pin serial port to PLC MPI 9-pin port communication cable.

hinddhindsa

Member
Join Date
Mar 2013
Location
www.plckart.com
Posts
193
Dear friends .

I have is CP5711 siemens , it is having USB cable from Laptop to CP5711 Port. but does not have a cable from Other side (serial) of cp5711 to plc port.

Can your please provide me the cable pin out so i can build the cable for this.

Thank You very much in advance.
 
Cp 5711

The other end of the CP5711 is not a serial port, it is the MPI/DP port.

Mainly it uses pins, 3 & 8

Pin 3 is signal B
Pin 8 is Signal A

Be careful not connect an RS 232 Cable on that port.