Problem Configuring Ethernet for Schneider M340 PLC

dev78386

Supporting Member
Join Date
Sep 2016
Location
Australia
Posts
24
Hi guys,

I am using BMXP341000 processor and a NOC04001 Communication module. I have seen some you tube videos where people configuring the ethernet are choosing (CPU) instead of default NOE (I am new to this and have no idea). I am doing my final year engineering project and trying to build a test bench using Schneider M340 PLC. Can some one help me to fix the issue looking at the error message I have attached.

Kind regards
Immanuel

IMG_2438.jpg
 
where it says FTP and HTTP access right behind the error message in the screenshot, change DISABLED to ENABLED for "firmware upgrade & FDR (FTP/TFTP)" and "web access (HTTP)"

the message is telling you that the module doesn't support having FTP/TFTP or HTTP disabled.
 

Similar Topics

Hello Everybody, I am new here and I would like you to help figure out a problem, I recently installed a data acquisition unit, Yokogawa MW100...
Replies
0
Views
2,085
I configured a file in simatic manager.And I select plc (with mouse) and object properties (with right click).One window opened (title object...
Replies
2
Views
1,998
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
Replies
0
Views
33
Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
Replies
3
Views
155
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
Replies
3
Views
134
Back
Top Bottom