Some years ago I ran into an interesting problem at a fish byproduct processing plant. Basically these guys cooked up byproduct from commercial fishermen and extracted oil and fish meal. (Yes the process STANK like nothing else!!!)
The extraction process was done by feeding the cooked up fish mush into a large (about 2m dia * 3m long) horizontal axis centrifuge. I forget how fast it ran but from memory it had about a 40kW standard induction motor that was originally star-delta started, but someone had retrofitted a Soft-Starter. Unfortunately the SS increased the startup ramp time so the thermal O/L would trip about 20% of the time.
So I suggested a VSD. Customer grumbles at the cost. Month later he rings and asks me to install it in a hurry. Arrive ; S/S has died, centrifuge no starts at all.
A few hours later I have I nice new AB 1336 Classic VSD in place and she starts up and runs like a dream. The owner is especially pleased that he can now fine tune the speed of the drum to suit the type of fish he is processing...and I put really long decel times in to prevent OverVolt trips due to the drum energy being driven back into the VSD Bus. Test it all out and it works fine.
Next day...problems at the fish plant. VSD is tripping out on OverVolt!!! Watch the operator start up; gets to target speed and all is well. About 2 minutes later, with NO operator change of speed the drive trips on OverVolt!
OK dudes...first in with the correct answer wins this weeks' smartypants award!!
The extraction process was done by feeding the cooked up fish mush into a large (about 2m dia * 3m long) horizontal axis centrifuge. I forget how fast it ran but from memory it had about a 40kW standard induction motor that was originally star-delta started, but someone had retrofitted a Soft-Starter. Unfortunately the SS increased the startup ramp time so the thermal O/L would trip about 20% of the time.
So I suggested a VSD. Customer grumbles at the cost. Month later he rings and asks me to install it in a hurry. Arrive ; S/S has died, centrifuge no starts at all.
A few hours later I have I nice new AB 1336 Classic VSD in place and she starts up and runs like a dream. The owner is especially pleased that he can now fine tune the speed of the drum to suit the type of fish he is processing...and I put really long decel times in to prevent OverVolt trips due to the drum energy being driven back into the VSD Bus. Test it all out and it works fine.
Next day...problems at the fish plant. VSD is tripping out on OverVolt!!! Watch the operator start up; gets to target speed and all is well. About 2 minutes later, with NO operator change of speed the drive trips on OverVolt!
OK dudes...first in with the correct answer wins this weeks' smartypants award!!