I use PLC 5/40 and try to use Flex IO as a remote IO with 32 point IO modules.
Flex layout is show below
1. 1794-ASB/E
2. 1794-IV32
3. 1794-OV32
I use standard 32 pt mode. (Dip Switch S1-1 is off)
On RSLogix5 PLC5 see only 16 LSB points of module.
It doesn't see 16 MSB points of 32 modules.
In 1794-ASB/E, it said if we set S1-1 to off, we can use standard 32 pt mode but you need to use rack number 40 and upper which is not support by PLC5.
Is this true?
If the answer is yes, Is there any way to config 32 point modules work with PLC5?
By the way, Is there anyone used to try to use block transfer with 32 points digital module?