Wondering if there is a certain number of Analog/VHSC cards that can be placed into a PLC-5 14-slot and 17-slot racks before you start to put to much strain on the power supply for the rack. Or if this is even an issue with PLC-5 racks, I know that there is with Modicon Quantum racks and think this probably still holds true.
 
I've never worried about it with the big 1771-P7 power supplies, but I you could overload one of the smaller slot-mounted ones.

I'd have to get out the Installation Instructions for each module and start tallying up their loads.

For example, the 1771-IFE Analog Input modules draws 500 mA from the 5V bus, and the 1771-VHSC draws 650 mA.

Because the 1771-P7 can supply up to 16A, you can pretty much use any module mix you like.

The smaller 1771-P3 (3A) or 1771-P4/P5/P5E (8A) might not be able to handle a larger chassis full of higher-draw modules.
 

Similar Topics

Hi I need to add analog inputs to a machine but the PLC rack is full of digital I/O,Sercos and ethernet comms cards and the electircal cabinet...
Replies
11
Views
5,020
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
113
I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
Replies
3
Views
512
My customer has a PLC-5/80 with 20+ RIO racks. They've asked me to remove one of the racks without shutting the system down. Can I set the...
Replies
15
Views
3,977
Hi All Need to relocate a DirectLogic 305 into a 19" rack. So need a 3U 150mm deep tophat shaped panel. We have some in the simulator but these...
Replies
5
Views
2,175
Back
Top Bottom