Plc 5 q

On the left hand side of RSL 5 is your tree. If you scroll down just below your data files is a branch called force files, one for outputs and one for inputs. If you open these data tables then you scroll through them any bit with a 1 or 0 is forced.

RSL5000 has a search function which is faster, but I have not seen anything like that in PLC5.
 
And then once you see a forced item in the force files you can right click and choose Find All to locate it in the logic.

The PLC-5 and SLC 500 do not have a search for forces option like the 5000.

OG
 