1762IF4 not reading the full range

jmason

Member
Join Date
Sep 2018
Location
easton Pa
Posts
5
Having an issue with An AB 1762-IF4 .
I am trying to read a 0-10 VDC signal but only seeing counts up to 37762
I have checked the input voltages and they are reading correct with a DVM.

the system is a load cell set up for 0-10vdc
0-5 VDC = 0 -5000 and 5-10vdc 0 +5000.
Any assistance would be great.
Thank you
Jay
 
Question
1762-IF4 or 1762IF4 Analog Input Data Format.
Answer
Raw/Proportional
Data Table Value Voltage/Current Value
32767 10.5 Volts
31206 10 Volts
0 0
-31206 -10 Volts
-32767 -10.5 Volts
32767 21 mA
31206 20 mA
6241 4 mA
0 0 mA
Scaled for PID
Data Table Value Voltage/Current Value
16793 10.5 Volts
16383 10 Volts
8192 0
0 -10 Volts
-410 Less than -10 Volts
17407 21 mA
16383 20 mA
0 4 mA
-819 Less than 4 mA

but only seeing counts up to 37762
Really??

See above for raw data values
 

Similar Topics

Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
Replies
1
Views
27
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
77
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
Replies
9
Views
229
Dear all, I don't know why setup of password became challenging and weird. After setting up the password and try to upload the ladder from the plc...
Replies
3
Views
171
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
373
Back
Top Bottom