Ok, I’m starting to get this AD (D not B) thing,

Over all it seems to be a good choice for a PLC, just DIFFERENT then AB or Siemens, haven’t found anything that it can’t do, just finding out more that I can’t...

This is what I am trying to do (in short)

Using 7 DL06’s
6 of them writing over the ethernet to the 'main' (got that part done)
When a input goes high (in 1 of the six) it sets a bit in the main, when it goes low it clears the bit (got that part)

Now for the questions,
What options do I have?, the way that I have it, is not the best way and before I spend a week programming, I would like to look at different ways?

The way that I am doing it is,
For each input I am creating a WX, by using a LDA...that’s one thing that is not very clear is the addressing of the memory O40600 is what I am loading (that is coming from C0, I think), I think that it would be better (if I continue to use this method) I would be better off loading the inputs to a word then if that word is >1 sending that word to the 'main', then I would only have one WX

I know that C100-117 = VC100-117 etc (and BTW who the hell came up with 18 bits and then you can’t use 2 of them?), but how would address that in the LDA? Would that be O40604?

Or....You tell me, what do you think?, How would you do it?,

Many Thanks
 
You have the adressing of the word which contains C100-C117. That's 16 bits not 18, the base is octal. If you are confused as to the addressing check the CPU manual beginning with the section on 'PLC Numbering Systems'.


You mention 'inputs' but then refer to control relays (C). Which are you sending? Inputs, addressed as words, start at V0400 for X0-X17 You don't need to copy then to control relays. You could actually send the state of all your inputs in 1 WX. Just continously send them else you won't send an 'all off' when none are on.
 
Thanks Bernie

bernie_carlton said:
You have the adressing of the word which contains C100-C117. That's 16 bits not 18, the base is octal. If you are confused as to the addressing check the CPU manual beginning with the section on 'PLC Numbering Systems'.

I can not count, I see that now o_O o_O stupid..stupid



bernie_carlton said:
You mention 'inputs' but then refer to control relays (C). Which are you sending? Inputs, addressed as words, start at V0400 for X0-X17 You don't need to copy then to control relays. You could actually send the state of all your inputs in 1 WX. Just continously send them else you won't send an 'all off' when none are on.

And yes I was moving the inputs to a CR.

A continous send?, I was told that a continous send would slow down the network? so only do a send on a change of state
 
bernie_carlton said:
You mention 'inputs' but then refer to control relays (C). Which are you sending? Inputs, addressed as words, start at V0400 for X0-X17 You don't need to copy then to control relays. You could actually send the state of all your inputs in 1 WX. Just continously send them else you won't send an 'all off' when none are on.

One more thing then I will go back to the books, was this a type error V40400?
 
For 'change of state' keep a 'previously sent' image of the inputs and compare that to the current. Only send on a difference. Your statement of 'not equal to zero' would not tranmit the transition from 'some bits on' to 'no bits on'.
 

Similar Topics

Hi, Mostly AB guy here with a little Koyo experience, but all of its digital. I get handed three analog I/O cards and asked to prove that they...
Replies
6
Views
495
Hi all, I am making a test rig to be able to wire in any DL06 (or DL05) And create a HMI in red lions crimson 3.1 to test all the inputs and...
Replies
4
Views
927
I have a Cmore screen which is communicating to the DL06 in BCD and need to create a timer that works in real numbers for a test, I simply need to...
Replies
3
Views
2,122
I have a client that has many Automation Direct DL06 PLCs for a municipal water/wastewater system. When there is a power outage, one of the sites...
Replies
4
Views
2,438
Hey everyone, Working on a system with a Koyo DL06 processor and it's my first experience with them. I have DirectSoft 6 and we got the program...
Replies
5
Views
2,313
Back
Top Bottom