AB PLC and WAGO field bus coupler
Hi experts,

In our automation machine, we are using Allen bradley SLC 05 PLC and this PLC is linked to WAGO device net field bus coupler (750-306).
Sometimes suddenly machine stopped .I checked and found, on that WAGO field bus coupler have an overflow indication(red lit) blinking.
After that ,we need to shutdown and restart the whole system, then can run.

Please advise why the overflow indicator lit. Is it the PLC memory full or what?
 
You might be a victim of the infamous "Wago Wiggle".
I had an OEM account who used these by the dozens, and got burned because of poor contact between modules.
The answer to the Wago Wiggle is to ensure that the modules are clamped or gripped together, horizontally, so that the contacts always are forced together.
Good Luck.
 
your AB is too fast with sending messages.
the overflow comes from garbled messages and the wago can not receive more. The overflow is an overflow from the incoming buffer.
 

Similar Topics

Hi experts, In our automation machine, we are using Allen bradley SLC 05 PLC and this PLC is linked to WAGO device net field bus coupler...
Replies
0
Views
3,716
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
98
Does anyone has and wants to sell wago plc used or new. It's very difficult to find any wago plc and the estimate time from any site is around...
Replies
0
Views
528
I am having the shop guys load the wago plcs that we are shipping w/ the .img file via the plc built in web page. It appears as if most everything...
Replies
0
Views
703
Hi all, I'm trying to connect my WAGO PLC to multiple databases. It is currently connected to a single MySQL database using the library...
Replies
0
Views
908
Back
Top Bottom