Hello,

I'm running into an issue with how to resolve an indexed data array ADD in a SLC 5/5 to a Compactlogix 1769 L33ER conversion process.

I get a PCE error on the rung as "invalid expression or tag." I vaguely follow what's going on in the SLC. It's sampling a flow every certain seconds and adding to that index. I'm looking for suggestions on an easy way(or any way) to translate this to the compactlogix.

I get that the F (F33 0-256) is the array file of samples. [N7:7]:[N7:6] where 7 is the file index and 6 is the index counter.

Attached are the SLC and Compactlogix rungs top and bottom respectively.

Any ideas from you all out there is really appreciated!
 
In the Compact Logix, wouldn't you have to change the address to

F[N7_7].[N7_6]

or maybe you have to create F33 with 255 elements and an F34 with 255 elements and then write the tag as F33[N7_6] and F34[N7_6], respectively.
 
Last edited:
you must first cerate an integer array tag "N7[512]
then you can copy the data into it the addressing format is different
when you copy a Float type to and integer type each float word will take 2 integers on the copy command.
 
Would this not work?
I've not done too much with respect to arrays, I also find the conversion tool causes more problems than its worth (would'nt use it myself).


The n7[7] and n7[6] arrays need to be increased to suit, the 'file and index' are aliased to the n7[7] and n7[6] arrays respectively and the source1 and 2 are REALS.


I can't try it out as I don't have access to a plc at the moment so I may be shooting in the dark.


Forgot to add source1 should be aliased to f8[16]



Steve

Capture.JPG
 
Last edited:
N7 would be an integer array
N7[6] - N7[7] are indexed elements of the same array
I assume that Sourc1 and Source 2 are both integers as well
data type is important as to how they are handled
I would need to see the ladder code
I knw the conversions are not very good I ran into that years ago converting a PLC2 to a PLC5 when they first came out I spent about 2 weeks chasing down and fixing the conversion errors
 
No source1 & 2 would be reals the n7 array would be type INT, the result I invisaged would be (if translated back to Logix500) the equivalent of F[n7:7]:[n7:6]



Steve
 
you could use reals as an index best practice an index should be integer
array N7 element 6 would hold the hole number of the result and N7element 7 would hold the decimal part of the number.
the copy used 2 consecutive elements in the array
A real 123.456 would be N7[6] = 123 and N7[7] would be 456
this is why if possible you should never mix data types
 

Similar Topics

As per manual i was tested with PLC on below program. But not any changes using swap instruction. plz help
Replies
3
Views
1,995
I have upgraded an old RS500 project to Studio 5000, it has thrown multiple errors which I am currently working through. I have looked through...
Replies
8
Views
1,724
Hello guys, I use Tia Portal V16. What is the best way to change the indexed HMI tags when I change the format of an Udt in my plc program...
Replies
0
Views
1,308
Hello, I am doing a PLC5 to 1756 L81 conversion. I have an issue with what looks like an indexed array bit in the PLC 5 that I am unsure of how...
Replies
1
Views
1,272
I am trying to use indexed addressing to store a long series of bits in a "file" via a bit shift left function in RSLogix 500. The file I want to...
Replies
8
Views
3,899
Back
Top Bottom