Quote:
Originally Posted by GaryS View Post
I would be concerned about the length of wire with any analog signal
If he does this as 2 wire, loop powered 4-20mA with a single power supply in the receiver panel (the conventional manner), then a 400 foot run is nothing to 4-20mA. Absolutely no signal loss.



I've seen 4-20mA cable runs of over a mile (1.6Km) at the mills that have run for years with no problem at all.


Conventional 4-20mA is VERY robust.


I have no idea if the 2 supply thing will even work, but to me it isn't worth bothering with because loop powered, 2 wire, passive 4-20mA transmitters were designed to work with a remote power supply at the receiver.



2 wire cabling runs from receiver panel to the field is the prime driver for 4-20mA; the wire break fault detection at 0mA is just a side benefit.
  Reply With Quote
Old December 3rd, 2019, 01:21 PM   #17
m_turk
Member
Croatia

m_turk is offline
 
Join Date: Jan 2008
Location: ZG
Posts: 200
Quote:
Originally Posted by danw View Post
If he does this as 2 wire, loop powered 4-20mA with a single power supply in the receiver panel (the conventional manner), then a 400 foot run is nothing to 4-20mA. Absolutely no signal loss.



I've seen 4-20mA cable runs of over a mile (1.6Km) at the mills that have run for years with no problem at all.


Conventional 4-20mA is VERY robust.


I have no idea if the 2 supply thing will even work, but to me it isn't worth bothering with because loop powered, 2 wire, passive 4-20mA transmitters were designed to work with a remote power supply at the receiver.



2 wire cabling runs from receiver panel to the field is the prime driver for 4-20mA; the wire break fault detection at 0mA is just a side benefit.
+1
Until 300m and if on the same "earth" I don't even think about it as an issue..
If it is another building or longer I'd consider some separators or protection, barriers but 100m is nothing...

And, I'd use the plc power supply too if possible, less possible problems..
  Reply With Quote
Old December 3rd, 2019, 02:02 PM   #18
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,038
It's a bit of a mess before it gets off the ground. Wouldn't some form of remote IO be a better solution.
  Reply With Quote
Old December 3rd, 2019, 03:23 PM   #19
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 3,095
Quote:
Originally Posted by janner_10 View Post
It's a bit of a mess before it gets off the ground. Wouldn't some form of remote IO be a better solution.
The OP needs a shielded, twisted pair cable for each transmitter. In my world, that isn't messy, it's conventional and any instrument guy with a DVM can troubleshoot it.

Yes, he could do remote I/O, but for how many signals/transmitters? There's a point where ROI comes into play.
  Reply With Quote
Old December 5th, 2019, 12:51 AM   #20
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,038
You have analogue signals 100m apart, I would say you've past the point of getting remote IO already, simply on future proofing and trouble shooting grounds alone.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
To Latch Or Not To Latch BOWRIDER LIVE PLC Questions And Answers 43 October 21st, 2015 05:19 AM
Universal power supplies wanted. elevmike LIVE PLC Questions And Answers 5 February 26th, 2006 01:22 PM
Analogue Inputs - Sink, Source, Help! Yabadabadoo LIVE PLC Questions And Answers 14 January 26th, 2005 01:48 PM
DC supplies for loop power godfrey LIVE PLC Questions And Answers 2 November 2nd, 2004 09:19 PM
DC Power Supplies Rookie_Engineer LIVE PLC Questions And Answers 5 April 29th, 2003 04:29 PM


All times are GMT -4. The time now is 01:01 PM.


.