I need a little help setting up some 1771 ASB adaptors and chassis. I have a PLC 5 system with 4 RIO chassis which was never finished when installed. One of the RIO chassis is set up and working correctly (Racks 1,2,3). The other 3 RIO chassis (in substations) haven't been setup, but code was written in the ladder logic, so I know which logical racks need to be set up in each substation.
How do I set up the switches for the ASB's for the rack numbers.
I have:
ASB Sub 2 - Racks 6 & 7
ASB Sub 3 - Racks 4 & 5
ASB Sub 4 - Racks 10 & 11.
I under stand SW1 1-6 is the IO Rack number, but is this set to the first logical rack in that chassis? I.e. ASB Sub 2, I would set to 111001, then the PLC will know that this chassis starts at logical rack 6 so the next logical rack will be 7?
Sorry for the long winded post, im a bit confused here.
I need a little help setting up some 1771 ASB adaptors and chassis. I have a PLC 5 system with 4 RIO chassis which was never finished when installed. One of the RIO chassis is set up and working correctly (Racks 1,2,3). The other 3 RIO chassis (in substations) haven't been setup, but code was written in the ladder logic, so I know which logical racks need to be set up in each substation.