plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old September 23rd, 2022, 11:25 AM   #1
Robb B
Canada
Robb B is offline
Fault on 1746 L551C
Happy Friday everyone!
I recently installed a new module, 1746 NIO4I, into the last slot on this chassis. Got the normal IO mismatch fault, added the module via "Read IO", saved the configuration, downloaded it to the processor, switched back to run mode, everything ran fine overnight. Today, I went to plug the terminal block into the card, and got faults. I've attached the two faults, and have since gotten them cleared by use of "Clear Faults" a few times. Just wondering if anyone else had issues like this? Possibly defective board? It was in a "Factory Sealed" box, looked to be authentic AB.
Last edited by Robb B; September 23rd, 2022 at 11:56 AM. Reason: I plugged the terminal block (not the module itself) in with PLC power on
Old September 23rd, 2022, 11:46 AM   #2
Ken Roach
United States
Ken Roach is offline
Ken Roach's Avatar
Did you insert the module with the backplane powered up ? That could have damaged it all by itself.
I would do a cleanup of the backplane and the module connectors with canned air and isopropyl alcohol to start. There almost certainly is no software or firmware workaround.
Old September 23rd, 2022, 11:57 AM   #3
Robb B
Canada
Robb B is offline
I defnitely did NOT insert the module with the power on. I am very aware SLC cards are not hot swappable, we also have ControlLogix racks here, which I have hotswapped just fine, but I still prefer to do them dead, too.
You mention cleaning the backplane, I wonder if it's possible some debris got in there while installing. I am usually very careful with these cards, even wearing the anti-static wrist band. I was concerned primarily because the module had already been installed for over 24 hrs and no faults (other than the initial IO mismatch, which was fixed easily). I only got this error when I went to plug the terminal block into the card. I understood the terminal block to be OK to "hot swap" but not the module.
Old September 23rd, 2022, 12:38 PM   #4
Ken Roach
United States
Ken Roach's Avatar
Thanks for those details ! I agree that you've probably done everything correctly.
Can you put a scope on the DC power and DC common on the analog wiring ? A very noisy signal can bleed over and interfere with the backplane chip interface sometimes, which leads to the "stuck runtime" and "wrong ID" faults.
You have two modules of the same sort, correct ? I suppose swapping their positions will provide a datapoint about whether the problem is the module itself, or the slot or wiring.
Old September 23rd, 2022, 12:42 PM   #5
Robb B
Canada
Robb B is offline
I don't have a scope. I do have two of the same cards side by side, as well as a spare of it. If I get a chance to power down the rack for cleaning, I can try swapping cards in the slots. Would a wiring fault cause similar errors? I triple checked my wiring before plugging the terminal block in, so I really don't think there's any problems. I wonder if I didn't just push a bit hard and temporarily unseated the card from the back plane. It is the farthest card out, so maybe a small flexing opened a contact briefly. I'll try not to lose too much sleep over this one!
Old September 24th, 2022, 12:45 AM   #6
James Mcquade
United States
James Mcquade is offline
just some ideas.
does the rack size match in the config table to what is actually there?
is the power supply big enough for the new card?
will the plc support the new card / revision?
power down the plc, reseat all cards 2 times, then remove the power supply and reseat it 2 times also. i has solved the same issue.
hope this helps
james
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
GSV and SSV nur11 LIVE PLC Questions And Answers 4 June 14th, 2021 09:18 AM
1769-AENTR Type 3 Code 16 Fault Help Bysons LIVE PLC Questions And Answers 3 May 25th, 2021 07:31 PM
Stupid question Alert For SMC Flex Soft Starter. Bob O LIVE PLC Questions And Answers 8 August 28th, 2017 01:15 PM
ET200S - ignore loss of IM-151 cjd1965 LIVE PLC Questions And Answers 10 May 28th, 2013 11:27 PM
TP177B + S7-300 on Profibus: No output happyhippo LIVE PLC Questions And Answers 23 May 15th, 2008 07:31 AM