plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old January 13th, 2022, 12:31 PM   #1
wsptay
United States
wsptay is offline
Plc 5
How many control blocks / messages can you have on one processor for plc 5?
Old January 13th, 2022, 12:38 PM   #2
Operaghost
United States
Operaghost is offline
Operaghost's Avatar
Memory is the only limit.
OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
Old January 13th, 2022, 12:42 PM   #3
wsptay
United States
wsptay is offline
Do you know off hand how much memory does one message take?
Old January 13th, 2022, 01:11 PM   #4
Jim3846
United States
Jim3846 is offline
I know in contrologix there was a connection limit for every processor.
Ethernet connection MSG was 1 connection.
HMI server sometimes have multiply connection per plc.
Total connections are in a manual.
I even think there is a limit in a SLC500 plc
If you look in the PLC5 instruction pdf I think it gives how much memory a MSG instruction takes plus the data table that your sending.
But PLC-5 I do not see it. I think your limited by if your msg works all the time without locking the processor up. So its a put it in and see if it works. Just remember PLC5 is not a fast processor, scan time 20-40msec usually is the fastest i have seen. Then if your doing Ethernet its better to use an enhanced PLC5. Not sure about the non enhanced PLC5.
Old January 13th, 2022, 01:33 PM   #5
Operaghost
United States
Operaghost's Avatar
Quote:
It varies depending on what CPU you are using and if your messages are going over Ethernet (more memory) or another network type. The MSG uses Program memory for storing the instruction and Data memory for storing the configuration of the message.
Worst case scenario is using an MG data type over Ethernet. Each MG data block consumes 56 words of data table memory. Ethernet requires two of these MG blocks for each message. So, 112 words of data table memory would be used for each message. Then you still must program the logic. It looks like the MSG instruction requires 7 words of Program memory. That is what I am observing.
So, if I had 100 messages, we would be looking at 11.2k of memory for the configuration data. If I had a PLC-5/40 controller, it has a total of 48k memory for both data and logic.
If you are not using Ethernet, cut that number in half.
OG
__________________
Old January 13th, 2022, 02:00 PM   #6
Operaghost
United States
Operaghost's Avatar
"Connections" as we know them in the Logix 5000 don't tend to be the issue with the PLC-5. Usually, it is the message buffers that might be an issue. Sort of a similar concept though.
The PLC-5 has message buffers for each channel where it will queue up messages while they wait to be sent. Issues can arise when you are trying to send more data faster than the network can handle. As a result, the messages buffers can fill up.
The size of those buffers varies by connection type. The DH+ buffers I believe can hold thirty messages for each channel. Not sure exactly what Ethernet supports. I recall it being sixty-four.
Ideally if I had a bunch of messages, I would try to stage them in a sequence so they aren't all trying to send at the same time.
OG
__________________
Old January 13th, 2022, 04:51 PM   #7
Jim3846
United States
Jim3846 is offline
Quote:
OG
That is typically what i see in PLC5 programs. Don't overwhelm the PLC is the rule.
Old January 14th, 2022, 01:30 PM   #8
mylespetro
Supporting Member
Canada
mylespetro is offline
mylespetro's Avatar
Just used Rockwell's recommended message staging procedure on a ControlLogix handling a large amount of data literally earlier this morning, replaced an uncontrolled/rapid-fire messaging and it worked great. Processor used to get overloaded very easily and freeze requiring someone to pull the processor and reseat it, now it's communicating just as fast but with only one connection at a time.
I actually adapted the message control program from a PLC-5/RSLogix5 template sent to me by my local Rockwell representative into a Logix5000 equivalent.
Old January 14th, 2022, 01:48 PM   #9
mylespetro
Supporting Member
Canada
mylespetro's Avatar
For anyone interested, I've attached a zip file of Rockwell's recommended message control method, there's a KB TechNote PDF as well as a PLC5 and a Logix5000 program.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Mitsubishi PLC died. Twice. JRoss LIVE PLC Questions And Answers 13 October 16th, 2019 06:45 PM
More questions about RSemulator, PLC network, and career path... timcph2008 LIVE PLC Questions And Answers 0 March 8th, 2018 01:04 PM
PLC Update - Back Issues Collection Now Available! Phil Melore LIVE PLC Questions And Answers 11 October 22nd, 2015 04:17 AM
Siemens PLC won't auto-run after power-up Lamboom LIVE PLC Questions And Answers 5 August 19th, 2014 06:32 PM
PC to PLC Protocol TheRixta LIVE PLC Questions And Answers 13 December 17th, 2008 02:56 PM