Micrologix RTD 1762-IR4 Reads as 0 Ohms before correcting
I have a Micrologix 1400 with an 1762-IR4 RTD. I use it to read airbag resistance on seats on an assembly line. I am often getting into a situation where it is reading as a short circuit, when there is not a short. Then it kind of just goes away after minutes. I can't find a rhyme or reason to it. Any ideas would be appreciated. When in this state, any resistance applied across the RTD inputs doesn't read correctly.
Old January 14th, 2022, 07:54 PM   #2
danw
United States
danw is offline
danw's Avatar
I am assuming that this used to work properly (no false zero Ohms readings). It sounds like you have tested the resistance module with a known resistance when 'the readings' are acting uip and that the module does not read the correct value of the test resistance.
The highest probablility is that the resistance input module is bad. Then there are far less likely things like intermittent backplane connections, or an intermittent power supply. It is highly unlikely that the PLC program is executing code that reports some other variable unless someone has been working on the program recently,
Replace the resistance input module.
Old January 14th, 2022, 08:31 PM   #3
James Mcquade
United States
James Mcquade is offline
Welcome to the forum.
be sure to check the rtd requirements as far as the in series resistance required for testing purposes. you also MUST have multiple resistance masters to check the rtd circuitry for quality assurance. Have you done a gage r & r study?
james
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
MicroLogix 1400 RTD Module Jason Ozolins LIVE PLC Questions And Answers 8 June 14th, 2016 04:12 PM
Device net reads 0 ohms? dhracer3 LIVE PLC Questions And Answers 2 November 14th, 2015 09:10 AM
micrologix 1400 and 1762 if4 heroek LIVE PLC Questions And Answers 2 June 26th, 2013 05:39 AM
micrologix 1200 input 1762 if4 module mehmetyil_99 LIVE PLC Questions And Answers 6 November 22nd, 2007 03:19 AM
MicroLogix 1500 RTD Module RobertG LIVE PLC Questions And Answers 0 August 31st, 2004 07:08 PM