Hello,

I just recently flashed a L7 processor from version 20 to version 32 and my sercos card is flashing the green ok status LED. When i go into module properties it says it is in "Program Mode" Help would be appreciated
 
Welcome to the PLCTalk forum community !

Did you also update the firmware in your 1756-M08SE SERCOS motion module ? In general, motion modules need to match the firmware of the controller, and version 32.001 is available for download for the 1756-M08SE.
 
Thanks Ken for the help,

And yes i did flash the module up to Version 32 as well. The ring light and the other status LED are solid green but the ok light is flashing. And i looked on rockwells forums and all they tell me is that the module is "not configured" which cant be true.

I would like the point out that the drives that i am controlling are in an off state at the moment for maintenance. Would this problem resolve itself once we boot those back up?

Again thanks for all the assistance
 
I believe you are correct that this will likely take care of itself when the drives are powered up. I suspect the SERCOS card is attempting to write parameters to and trigger phase transitions in drives that aren't responding. I wouldn't get too worried until the drives are available again.

Keith
 
We will be starting up soon and I’ll drop a follow up comment if this resolves the issues.

Thanks for all the help. It is very much appreciated.
 
Gentlemen,

I booted drives up and all issues were resolved. Thanks for the quick response and I definitely look forward to using this forum in the future.

"Do or Do not, There is no Try" -Yoda
 

Similar Topics

Hi all, I'm new to this site but have been programming for a long time. I have a situation where I need to disable 1 of 2 1756-M08SE modules...
Replies
2
Views
1,685
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
Replies
6
Views
135
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
127
Hi, Is it possible to for an RIO with Flex 5000 series module, e.g. 5094-AEN2TR, to communicate with an 1756-L72E processor.
Replies
1
Views
85
please using the usb can i assign any ip address that i want ?
Replies
4
Views
144
Back
Top Bottom