Allen Bradley 5/40L with local I/O extension

nfvtmeinc

Member
Join Date
Feb 2003
Location
Ohio
Posts
20
I am trying to autoconfigure a local I/O extension on an Allen Bradley PLC 5/40L. I have a 1771-alx adapter card in an AS2B series B
rack. I have verified all of the dip swithes on the adapter card and the rack and they are correct. Whenever I try to autoconfigure the local I/O extension it fails and tells me to be sure I have created an I/O status file. There is an I/O status file because the scanner channel will let me autoconfigure it. I am using allen Bradley Rslogic5 programming software. Would anyone have an ideas?

Thank you Doug Barnett
 
Doug

Using RSLogix, open Processor Status and select the Main tab. IO Status S16: should contain a value which is the file number of the I/O States file. If there is a 0 for the value, there is not a Status file. Choose an unused File Number and enter the number in S16. Then try to autoconfigure again.
 
If you have the proper configuration for channel2( Extended-Local I/O)
and have defined a diaganostic file using a unique unused integer file and defined the scan list the next thing you should do is clear the global inhibit bit. The global inhibit overrides the automatic configuration. You will need to clear the global inhibit bits for all chassis on the channel and then use the automatic configuration function. Clear the global inhibit bit from the processor status screen.

Roger
 

Similar Topics

Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
Replies
15
Views
229
Hello, Does anyone have one of these cables and willing to open the case so I can see the cable connections inside? 2707-NC5 I have sourced the...
Replies
3
Views
84
Currently trying to find: micrologix ethernet interface 1761-NET-ENI AIC to micrologix 761-CBL-AM00 Ser C cable These are used for micrologix...
Replies
3
Views
133
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
173
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
459
Back
Top Bottom