Can 5069-L33xx local rack be expanded?

skyfox

Lifetime Supporting Member
Join Date
Nov 2006
Location
CA
Posts
276
1768-L43 Local rack was expandable in to a 2nd Rack via an expansion cable. For an example;


PS ENET CPU I/O I/O I/O I/O [Expansion Cable] - Main Local Rack

PS I/O I/O I/O .... [END CAP] - Local Rack Expansion


Can the Same be done with 5069-L330xx series PLC's? I couldn't find any info that said it could or couldn't be done.


Thanks-
 
Don't think you can. At least if you put it into IAB and try to configure a second bank it won't let you like it lets 1769/1768 processors
 

Similar Topics

Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
Replies
8
Views
362
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
477
Hi all, have a project which requires reading a weigh head weight over ASCII. Never really touched ascii so struggling a bit. The weigh head is in...
Replies
11
Views
1,182
Hello, I have a laying out a system that will have a CompactLogix rack and I had a question on the power for the inputs and outputs. I was...
Replies
1
Views
340
I want to factory Reset my 5380 (5069-L310) I have here in home lab. Reason being I want to make a Internal How-To video for Setting the IP...
Replies
2
Views
438
Back
Top Bottom