I am trying to write an app in LabVIEW, where I can send CIP frames to EN2T module that represents socket MSGs. I'm using Send RR Data command with proper Class and Instance IDs for socket MSGs. And it's not working :confused: , I get a CIP response saying "Path segment error". I've read then that those MSGs must be send via backplane and cannot access the module via ethernet port, but is there a way to bypass it somehow :unsure: ? Thank you
 
Welcome to the PLCTalk forum community !

In general, "socket messaging" with the 1756-EN2T refers to manually-coded protocols that are not CIP.

You do need the CIP path to access the Backplane (port 1) and the Slot (Slots 0-16) of the ControlLogix.

The modern CompactLogix and the 1756-L8xE controllers with an integrated Ethernet port can use the Ethernet module as the endpoint of the CIP path, but the ControlLogix CPU's without an integrated Ethernet port need that last path segment.
 

Similar Topics

Hi Everybody, newbie here with PLCs, using a B&R plc. I'm playing with a printer and its tcp socket communication. Connection works fine if...
Replies
3
Views
140
Hi all, I have two questions I am hoping someone might have some information on. 1. I remembered reading somewhere on this forum that you could...
Replies
5
Views
186
Hello, I'm trying to setup a TCP connection from a Compactlogix 5069-L306ER to a TDI checkweigher to receive real-time weight data of the...
Replies
6
Views
314
I would like to communication with application installation in my printer server via TCP port 5450. i.e ., 71.16.40.200:5450 . How can i write...
Replies
1
Views
401
I'm hooking up a scale to an EWEB card on a 1756 PLC through ethernet/IP sockets, and I've run into an issue that seems to defy ladder logic. See...
Replies
9
Views
2,673
Back
Top Bottom