We have six NICs for Siemens 505 chassis at our place, and four are acting normally.
Two are not able to complete set-up. I have tried both the CTI Diag utility for Windows, and the 2572IPSET for DOS utility; they have similar but not identical results.
I am trying to set the cards to IP address 192.168.3.7x, and a router of 192.168.3.1, and a subnet mask of 255.255.255.0, and (default)port 1505 .
The bizarre part is that I can change the IP, router, port at will, and the change takes effect. However both cards will always reset their net masks.
The card does a READ to show me the present values, then I choose to WRITE, and it does a confirming READ. I will only show the netmask result here, as all other fields work fine.
Card1: using 2572IPSET
trial 1 WRITE 255.255.255.0 READ 10.53.0.22
trial 2 WRITE 255.255.255.0 READ 10.65.0.22
try IPSET /I (display only) reads 10.64.0.22
trial 3 using CTIDiag WRITE 255.255.255.0 READ 115.221.233.0
Card 2: using either
all trials WRITE 255.255.255.0 READ 10.20.0.22
I have also tried setting the mask to 0.0.0.0; results are same.
Yes I have tried with and without power cycle between the Write and another Read - no difference. Please recall that I have successfully configured four other cards, so I know what they should be doing.
The EEPROMS in the cards are both dated 1995; one is version 2.0, the other version 4.5. CTI tech support has suggested that the EEPROMS are 'fried', however this seems like a mighty selective failure for both cards to have almost identical problems. As well, the difference between reading the one with CTIDiag versus 2572IPSET is also exceeding strange.
I tried swapping the EEPROMS in from one of the newer cards, but I could not even go on-line with it then.
CTI want to sell me new rev. B cards to solve the problem.
Ideas, anyone?
Two are not able to complete set-up. I have tried both the CTI Diag utility for Windows, and the 2572IPSET for DOS utility; they have similar but not identical results.
I am trying to set the cards to IP address 192.168.3.7x, and a router of 192.168.3.1, and a subnet mask of 255.255.255.0, and (default)port 1505 .
The bizarre part is that I can change the IP, router, port at will, and the change takes effect. However both cards will always reset their net masks.
The card does a READ to show me the present values, then I choose to WRITE, and it does a confirming READ. I will only show the netmask result here, as all other fields work fine.
Card1: using 2572IPSET
trial 1 WRITE 255.255.255.0 READ 10.53.0.22
trial 2 WRITE 255.255.255.0 READ 10.65.0.22
try IPSET /I (display only) reads 10.64.0.22
trial 3 using CTIDiag WRITE 255.255.255.0 READ 115.221.233.0
Card 2: using either
all trials WRITE 255.255.255.0 READ 10.20.0.22
I have also tried setting the mask to 0.0.0.0; results are same.
Yes I have tried with and without power cycle between the Write and another Read - no difference. Please recall that I have successfully configured four other cards, so I know what they should be doing.
The EEPROMS in the cards are both dated 1995; one is version 2.0, the other version 4.5. CTI tech support has suggested that the EEPROMS are 'fried', however this seems like a mighty selective failure for both cards to have almost identical problems. As well, the difference between reading the one with CTIDiag versus 2572IPSET is also exceeding strange.
I tried swapping the EEPROMS in from one of the newer cards, but I could not even go on-line with it then.
CTI want to sell me new rev. B cards to solve the problem.
Ideas, anyone?