Rockwell Automation- Software Configured Safety Relays displayed on HMI's ?

Good Morning ,

I'm working on a safety project , and I'm thinking of using the
Guardmaster 440C-CR30 Software configured safety relay with the 440C-ENET Guardmaster Ethernet Plug-in module.

I would like to present the status of the safety circuit on a HMI. Does the 440C-CR30 allow to interface with a Panelview Plus HMI ? and what software do you use to to configure the 440C-CR30 ?

Thanks so much,
  Reply With Quote
Old July 16th, 2019, 08:01 AM   #2
jgreenewv
Lifetime Supporting Member + Moderator
United States

jgreenewv is offline
 
Join Date: Aug 2002
Location: New Mexico, USA
Posts: 240
I haven't used these yet, but I've seen several demos. Connected Components Workbench is used to program the 440C-CR30 relays. And yes, you can pull the info into a PanelView Plus for status display. The demos I've seen use the Ethernet plug-in module but I don't really have any technical details.
  Reply With Quote
Old July 16th, 2019, 08:09 AM   #3
Baker in Virginia
Member
United States

Baker in Virginia is offline
 
Join Date: Aug 2016
Location: Virginia
Posts: 248
Thanks ,

On a Panelview Plus , you can bring into the application , numerous PLC's as shortcuts and display information from each one , correct ?
  Reply With Quote
Old July 16th, 2019, 05:05 PM   #4
jgreenewv
Lifetime Supporting Member + Moderator
United States

jgreenewv is offline
 
Join Date: Aug 2002
Location: New Mexico, USA
Posts: 240
Quote:
Originally Posted by Baker in Virginia View Post
Thanks ,

On a Panelview Plus , you can bring into the application , numerous PLC's as shortcuts and display information from each one , correct ?
If the PanelView Plus is connected via Ethernet to multiple controllers, then yes, you should be able to create a shortcut to each controller and pull data from them. I can't recall if there are any limits to number of shortcuts per application.
  Reply With Quote
Old July 16th, 2019, 06:20 PM   #5
chavak
Member
Malaysia

chavak is offline
 
chavak's Avatar
 
Join Date: Jul 2002
Posts: 623
Sorry, I'm not a big fan of it. Used it some time ago.

Just ensure your components connected to it are safety rated. There are dedicated outputs which checks for components configured in place, by means of pulses output to it. I had a contactor and a valve bank power, connected to it, which gave out intermittent errors.

Regards
  Reply With Quote
Old July 17th, 2019, 05:21 AM   #6
jstolaruk
Lifetime Supporting Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,410
I've used that arrangement along with a non-safe PLC. Via Ethernet/IP, the PLC could monitor everything and the safety controller had non-safe inputs that the PLC could write to for clearing faults and resetting safety circuits. I don't see why an HMI could not do the same.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old July 17th, 2019, 12:52 PM   #7
Vlad Romanov
Member
United States

Vlad Romanov is offline
 
Join Date: Sep 2017
Location: Los Angeles
Posts: 138
You've gotten many answers, but I still wanted to add some info:

1. I would use a "master" or "line" PLC to pull in all of the data from all your safety devices.

2. I would create a single link from this PLC to the HMI which needs to have this information displayed.

3. If you need to display this data on multiple/different HMIs, I would create a produced/consumed or MSG based message from the "master" PLC to those who needed it and link to the data this way.

Also, the "standard" PanelView HMIs only allows a single reference point (it's very frustrating), so unless you have the more expensive "performance" edition, you may not be able to link to multiple PLCs.

Hope that helps...
__________________
I'm looking for PLC work... http://solisplc.com/
My Allen Bradley PLC Course: PLC Programming
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Safety Relays.... milmat1 LIVE PLC Questions And Answers 23 May 2nd, 2013 07:17 AM
Quick Rockwell Automation Software Question johnnysparks24 LIVE PLC Questions And Answers 4 June 14th, 2006 08:24 AM
Rockwell Software again... panic mode LIVE PLC Questions And Answers 16 October 20th, 2004 08:33 AM
RSLOGIX5 Rockwell Automation software - redundency PLC-hotbackup madhupraba LIVE PLC Questions And Answers 2 November 27th, 2003 07:27 PM


All times are GMT -5. The time now is 06:56 PM.


.