Disconnect on VFD output

Does anyone know if there is disconnect requirement for early break switches on the output side of a VFD for the controls?

We have talked about it once years ago and I can't find that thread. I want to say it wasn't a NEC requirement but a manufacture requirement.
__________________
There should be a minimum IQ before people can breed.

FS Eng (TÜV Rheinland, #11004/15, Machinery)
  Reply With Quote
Old July 16th, 2019, 12:52 PM   #2
Ken Moore
Lifetime Supporting Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: North, West, South Carolina
Posts: 2,622
Jeff,
I don't think it is a requirement, just good practice, if the disconnect is thrown when the drive is "working", the early break switch can send a "safe stop or safe torque off" signal to the drive a few milliseconds before the motor is disconnected from the drive.

On a couple of SIL-3 applications, I have seen Safe/Stop, Safe Torque off, used with an additional contactor downstream of the drive along with an encoder. On a Safety stop, the Safe Stop signal is sent to the drive, then if the shaft has not stopped in a certain time (milliseconds) the downstream contactor is opened. The goal is never open an downstream contactor under load if you can avoid it.

Last edited by Ken Moore; July 16th, 2019 at 12:56 PM.
  Reply With Quote
Old July 16th, 2019, 03:10 PM   #3
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,854
I would agree with Ken Moore that disabling the drive before the disconnect opens is preferable. However, todays IPMs do a pretty good job of protecting themselves. It's not like the bad old days when disconnecting a drive under load was almost a guaranteed blown drive.

Keith
  Reply With Quote
Old July 16th, 2019, 03:42 PM   #4
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,772
Quote:
Originally Posted by Ken Moore View Post
Jeff,
I don't think it is a requirement, just good practice, if the disconnect is thrown when the drive is "working", the early break switch can send a "safe stop or safe torque off" signal to the drive a few milliseconds before the motor is disconnected from the drive.

On a couple of SIL-3 applications, I have seen Safe/Stop, Safe Torque off, used with an additional contactor downstream of the drive along with an encoder. On a Safety stop, the Safe Stop signal is sent to the drive, then if the shaft has not stopped in a certain time (milliseconds) the downstream contactor is opened. The goal is never open an downstream contactor under load if you can avoid it.
Quote:
Originally Posted by kamenges View Post
I would agree with Ken Moore that disabling the drive before the disconnect opens is preferable. However, todays IPMs do a pretty good job of protecting themselves. It's not like the bad old days when disconnecting a drive under load was almost a guaranteed blown drive.

Keith
I agree on all counts; not a requirement, but a very good practice even though modern drives that use the latest generation of IPM have more protection than in days of yore. The arc that happens when you open a set of contacts under load can be damaging to transistors. The modern IPMs include suppression and shunt paths for that energy, but that can fail eventually.

All NEMA KS-1 designed knife switch type disconnects use handle operated aux contacts that are, by design, always early break compared to the main contacts. But if you use the low cost rotary type IEC disconnects where the aux contacts are driven off of the same cam as the mains, that is not always the case and you must make sure to order the early-break aux. contacts.
  Reply With Quote
Old July 16th, 2019, 04:19 PM   #5
JeffKiper
Lifetime Supporting Member + Moderator
United States

JeffKiper is offline
 
JeffKiper's Avatar
 
Join Date: Jun 2006
Location: Indiana
Posts: 2,195
You guys rock. I'm looking at an application with a few drives that will have field disconnects. Most of our small machines don't require field disconnects.
__________________
There should be a minimum IQ before people can breed.

FS Eng (TÜV Rheinland, #11004/15, Machinery)
  Reply With Quote
Old July 16th, 2019, 05:18 PM   #6
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,535
disconnects are required for all loads when they are more than 50ft away from the main power disconnect or are not within sight of the main disconnect when they are in that 50 ft range - NEC 70.

all our motor disconnect have aux contacts for feedback to the plc and scada systems.

james
  Reply With Quote
Old July 16th, 2019, 05:18 PM   #7
Nethop
Member
Canada

Nethop is offline
 
Join Date: Dec 2012
Location: BC
Posts: 18
We use Square D EIK032 switches in the local disconnect. DPDT. Wire one set to the enable cct. on the VFD and one set to the PLC for status.
  Reply With Quote
Old July 17th, 2019, 05:32 AM   #8
Ken Moore
Lifetime Supporting Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: North, West, South Carolina
Posts: 2,622
The disconnects are required, but....there is an exception in the code, if the facility has a formal lockout tagout policy/procedure.
  Reply With Quote
Old July 17th, 2019, 06:07 AM   #9
EICS
Member
Australia

EICS is offline
 
EICS's Avatar
 
Join Date: Dec 2008
Location: Melbourne
Posts: 195
What is a IPM ? Im an Aussie and have not heard that term?
Inverter power module im guessing. We call them IGBT's
  Reply With Quote
Old July 17th, 2019, 09:04 AM   #10
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 153
IPM: Intelligent Power Module.
basically IPM is same as IGBT motor drive module.
  Reply With Quote
Old July 17th, 2019, 09:49 AM   #11
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,854
Quote:
Originally posted by mike3475:

basically IPM is same as IGBT motor drive module.
...with the addition of protective devices and functions, reporting capability and interface isolation, all built into a single package.

Keith
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Increase VFD output voltage? einnh LIVE PLC Questions And Answers 7 July 13th, 2016 07:36 AM
[Logix] Analog mA going to -1.0 when VFD is called defcon.klaxon LIVE PLC Questions And Answers 13 February 26th, 2016 12:38 PM