SLC Battery Light is on... Why program isn't lost after weekend (turned off)

I was at a customer's today and 2 of 3 SLC 5/03s had the Battery Light on. I showed it to the maintenance guy and asked him when the last time the panel was powered down for an extended period of time. He said last weekend! I don't understand why they don't loose the program. The PLC power is off when the panel is powered down. Does a SLC 5/03 have EEPROM, non-volatile memory that I don't know about? I thought it was all volatile memory. What am I missing? I see municipal water and waste water plants with the same situation. They said the BATT light was not relevant to their setup.
  Reply With Quote
Unread July 16th, 2019, 11:20 PM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,262
Your SLC5/03 can have an EEPROM (its an option) see PDF

Also... The battery lite on just means its low, it can still hold the program. Depends on how low.

Quote:
IMPORTANT The SLC 5/03, 5/04, and 5/05 processors have a capacitor that provides at least
30 minutes of battery back-up while the battery is disconnected. Data in RAM
is not lost if the battery is replaced within 30 minutes.
Attached Files
File Type: pdf memoryinstall.pdf (122.9 KB, 4 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; July 16th, 2019 at 11:33 PM.
  Reply With Quote
Unread July 16th, 2019, 11:35 PM   #3
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,660
I have seen the capacitor hold the program for a full day.

Also, the battery light coming on means the battery has crossed a threshold. it doesn't mean it is fully depleted. It could still be functioning just at less than optimal capacity.

I used to tell people when that light comes on you may have up to two weeks before the battery fully dies.

So, EEPROM, capacitor, battery not dead yet. Three possibilities.

OG
  Reply With Quote
Unread July 17th, 2019, 01:11 PM   #4
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,629
the slc500 series has 2 methods of maintaining the program.

the primary method is the battery.

the secondary method is the internal capacitors on the plc card itself.
these are meant to hold the program long enough for you to turn the power off to the plc, remove the plc card, and replace the battery so you won't have to reload the program. I have known the caps to hold a test program for months.

please remember, this is not a guarantee they will work, so have the program backed up before killing the power or replacing the battery.

I had to have a 5/04 that lost its program everytime the power was lost.
the plc board went bad and the battery never saw the plc memory.
I had it repaired by teamsesco, its now on our stock room as a spare.

james
  Reply With Quote
Unread July 17th, 2019, 03:13 PM   #5
kwade
Member
United States

kwade is offline
 
Join Date: May 2013
Location: sc
Posts: 331
Quote:
Originally Posted by James Mcquade View Post
I had it repaired by teamsesco, its now on our stock room as a spare.

james
teamsesco site doesn't work, did we overload it?

Thank you, James for the 'word-of-mouth' reference to a somewhat local repairshop!
FYI: I did find a crawl at https://web.archive.org/web/20190511....com/about-us/

Last edited by kwade; July 17th, 2019 at 03:16 PM.
  Reply With Quote
Unread July 17th, 2019, 04:15 PM   #6
RoTaTech
Member
Canada

RoTaTech is offline
 
RoTaTech's Avatar
 
Join Date: May 2003
Location: Cobourg, ON, Canada
Posts: 389
Battery low

If the battery is loose, you may lose the program with power off.
__________________
"Nice mirror!" said Tom reflectively.
  Reply With Quote
Unread July 17th, 2019, 04:53 PM   #7
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,629
you maybe right, the site is down.

www.teamsesco.com
call 1-800-48-SESCO
(336) 662-0646

NOTE - teamsesco is a vendor I use to get plc components repaired and I am not associated with them.

I's sure there are others out there.

james
  Reply With Quote
Unread July 17th, 2019, 05:11 PM   #8
Blue Fox
Member
United Kingdom

Blue Fox is offline
 
Join Date: Feb 2013
Location: Basildon
Posts: 45
I had a site do similar recently all the battery lights were on - was a mixture of ab and Siemens. They weren’t concerned as wasn’t causing them a problem. Went back to the site a few weeks later and they said they seemed to have lost some mods a previous employee had done on one of the plcs. I had a quick look and compared online prog with a back up I had taken on a previous visit and found online had the mods missing. It was an s7-300 with an eprom however the mods had only been saved to the volatile memory and not the emotion so they lost them. I had to copy over my backup. All the other plcs had the versions on the cards which were correct. Moral of the story - don’t rely on the EPROMs unless site it has the correct programs!
  Reply With Quote
Unread July 17th, 2019, 05:21 PM   #9
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,660
Here is a telling comment.....
Quote:
Originally Posted by AutomationTechBrian View Post
I see municipal water and waste water plants with the same situation. They said the BATT light was not relevant to their setup.
That makes it sound like they are using the EEPROPM. RA calls it a UVPROM.

OG
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 500 BASIC Program Invalid Header Error kevgtown LIVE PLC Questions And Answers 0 March 29th, 2013 08:41 AM
Need Help with 1746-BAS error bfore LIVE PLC Questions And Answers 9 May 19th, 2011 04:24 PM
Program lost hramos_ LIVE PLC Questions And Answers 0 January 28th, 2010 05:20 PM
S7 312 program lost after power failure Thim LIVE PLC Questions And Answers 2 January 4th, 2010 02:20 PM