Old July 17th, 2019, 12:57 PM   #1
Old No. 7
Member
United States

Old No. 7 is offline
 
Join Date: Jun 2010
Location: Ohio
Posts: 131
Micrologix Messaging

Is there a "right" way to setup messaging between two ML1400 PLC's? Over the years we've done it several slightly different ways and usually get them to work.

We've done timers with the done bit triggering the message, we've had the done bit of one message trigger the next, we've had the error bit in parallel with the done bit, sometimes we use one-shots, and probably a dozen variations.

Does anyone have their tried and true bulletproof method they would like to share?
  Reply With Quote
Old July 17th, 2019, 01:13 PM   #2
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,219
Largely depends on the application and how often you want to transfer the data.
__________________
Go Hawks!!!
  Reply With Quote
Old July 17th, 2019, 01:50 PM   #3
penend
Member
United States

penend is offline
 
Join Date: Jul 2016
Location: Seattle
Posts: 4
this is a document for Logix 5000. page 23 is what you want to look at, you should be able to translate it for Logix 500

https://literature.rockwellautomatio...m012_-en-p.pdf

This is the most robust way to messages I have found.
  Reply With Quote
Old July 17th, 2019, 04:38 PM   #4
BlueAltezza
Member
United States

BlueAltezza is offline
 
Join Date: Nov 2012
Location: Cleveland, OH
Posts: 203
Quote:
Originally Posted by Firejo View Post
Largely depends on the application and how often you want to transfer the data.
^ This

I segregate the messages into groups like immediate, cyclic, and on demand.
I try to avoid immediate messages, but sometimes I need both PLCs to react to an event. When I do those, I don't allow the other messages to enable unless the immediate message instructions are done/idle. Old habit from 1500s, lol
The cyclic messages I set up to run after startup and just have a loop of them with the dn bit enabling the next message.
On demand when a value changes, so basically a neq and ons to trigger the message.

For the actual line logic I've done it a bunch of different ways and never noticed a change in performance or function.
I usually just default to three branches for consistency's sake:
Event (ons, dn from previous message, etc)
XIC msg dn -- XIO msg er -- XIO msg dn
XIC msg er -- XIO msg en -- XIO msg dn
  Reply With Quote
Old July 17th, 2019, 05:43 PM   #5
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 609
Quote:
Originally Posted by penend View Post
this is a document for Logix 5000. page 23 is what you want to look at, you should be able to translate it for Logix 500

https://literature.rockwellautomatio...m012_-en-p.pdf

This is the most robust way to messages I have found.
I do it similar to the above, except I never sequence the MSGs, I keep them independent with usually their own 250msec timers to keep the MSGs from firing faster than necessary to keep traffic down. The reason I don't sequence them is because I've seen some connection issues cause like 10 seconds to trigger the message to error out (.ER bit). In the case of the above logic, that one failed MSG now takes out all of your other MSGs since they are waiting for it to finish before starting themselves.

Last edited by rupej; July 17th, 2019 at 05:51 PM.
  Reply With Quote
Old July 17th, 2019, 06:07 PM   #6
penend
Member
United States

penend is offline
 
Join Date: Jul 2016
Location: Seattle
Posts: 4
You can change the timeout of the MSG so it will not hang, its set pretty high as default.
  Reply With Quote
Old July 17th, 2019, 08:20 PM   #7
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 609
^never noticed that... will have to check it out. Still, I've not found sequencing to be necessary with timers firing the messages individually. The other advantage is its easy to add another MSG instruction online without risking causing issues with the existing ones if you keep them separate and not sequenced.

Also, even if you set the timeout value low with it sequenced, one failed MSG is still holding up the rest, even if just slightly, and repeatedly until the connection is fixed. May or may not be a problem, but something that comes to mind.

Last edited by rupej; July 17th, 2019 at 08:24 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Messaging between a CompactLogix 533ER and a Micrologix 1100 soccernut43 LIVE PLC Questions And Answers 0 May 19th, 2015 06:28 AM
Kinetix 300 CIP messaging from Micrologix 1400 poj101 LIVE PLC Questions And Answers 11 October 13th, 2014 03:54 AM