panelview+400 and data logging

Join Date
Dec 2005
Location
melbourne
Posts
2
We have a system consisting of a ML1100 with an added 2 chan analog card and a panelview + 400.

The customer wants to keep records of a pressure switch readings (a 4-20 mA analog signal scaled in the ML1100 program to 0-400) which we have setup through the panelview saving the data to a storage card installed in the panelview itself.Then by converting the data log file from the storage card using the “digconverter” utility (free download from rockwell) the customer is able to read the data using a XL spreadsheet.

At this stage the data is logged as soon as the system is powered up it is logging 0-400 kPa.The customer is only interested in readings of over 250 kPa.

My question is can a trigger be set for the panelview to only log data when when the pressure switch reading is 250 kPa and above instead of logging from the initial power up ?.
 
I had a quick look and I would try to copy all the values of the data table above 250 into a new data table in the PLC. Then set the PV to log with a trigger of "change" not the periodic trigger. I think you should be able to then have it log every new value above 250..
Regards Alan Case
 
hi alan i think i have the guts of what your getting at.in the plc prog if i have a rung comparing the 0-400 readout for greater than or equal to 250 then when this is true move the 250 and above readout to another file and this will now be our log file.this will be triggered a "change" % and not periodic.
thankyou for your input alan
 
That is pretty well it. The panelview will look at the new file and any change of greater than 0% will be the trigger to write the log. May take a bit of trial and error but it should work.
Alan Case
 

Similar Topics

Has anyone migrated Proficy Historian data to a new server? I followed the guide to move all the data over, but when I run the utility, it stops...
Replies
0
Views
35
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
8
Views
173
Hi, Wy we log data in PLC using DLG instruction, when we have option to log data in HMI
Replies
1
Views
72
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
Replies
4
Views
95
I have an expression in a structured text routine of a Logix controller that looks more or less like the following: ResultInteger := Integer1 *...
Replies
13
Views
374
Back
Top Bottom