Soft Starter vs VFD

I've noticed a resurgence in Soft starters in custom Automation.

Besides them taking less space in a cabinet, are there any other pros and cons between the two?

Note: I know there are Ip67 VFD that can be mounted remotely


Thanks!
  Reply With Quote
Old October 22nd, 2018, 11:44 PM   #2
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 783
Soft starts generally require a bypass contactor to pull in after the motor is up to speed.
Some Soft Starts have the bypass contactor built in other require them to be supplied as an extra ( additional cost and room to mount it)
if don't need the change the motor speed them a soft start may be the way to go
but if you need variable speed them you need a VFD.

Although I do remember I think it was Louis- Allis made a drive for vibrating feed conveyors using a soft start and varying the phase angle of the scr's to hold the motor speed down. they used a special motor with class H insulation the motors all ran hot enough to cook on. That's the way they were designed.
  Reply With Quote
Old October 23rd, 2018, 01:28 AM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,945
Soft starters can take less space when you get above a certain size. They can cost quite a bit less, and they will generate much less heat (when up to speed and bypass contacts are closed).

Soft starters do not ramp smoothly (or much at all) when lightly loaded. Soft starters often have a limited duty cycle (amount of time spent ramping/using SCRs).
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old October 23rd, 2018, 05:09 AM   #4
PLC Pie Guy
Member
Canada

PLC Pie Guy is offline
 
PLC Pie Guy's Avatar
 
Join Date: Jun 2013
Location: Halifax
Posts: 705
There would be no noise generated from the soft starter. Lessening the need to run expensive drive cables to motors.
  Reply With Quote
Old October 23rd, 2018, 06:09 AM   #5
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 916
Power companies are getting a lot more strict on harmonics mitigation and rightly so. Harmonic currents cause voltage distortion for other customers and require oversizing of cables and transformers. If you have a large percentage of non linear loads on your site then mitigation measures are important.

If you dont need variable speed or slow ramps then use a DOL starter if it's small (<2kW) or soft start if its bigger.

Drives of course have their place; but they're not a panacea for **** poor mechanical design where an engineer doesn't know how to size a pump or fan or whatever correctly.
  Reply With Quote
Old October 23rd, 2018, 07:34 AM   #6
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
Soft starters and VFDs have been around for approximately the same time.
They are different devices for different applications, although you can use a VFD as a high-end soft-starter and soft-stopper. But since the price difference used to be so high, this was extremely rare. I have only seen it once. What I am saying, is that in the past you would not see VFDs being used where softstarters could have been used instead. So the scenario you describe does not exist IMO.

As for any new development in this area I would say that both soft-starters and VFDs are becoming more prevalent due to their dropping prices. But I definitely do not see a trend that soft-starters are being used in place of VFDs. Since VFDs are dropping more than soft-starters (relatively speaking) I would guess that it would be the other way around. Especially since you can get STO with most VFDs nowadays, that is an easy and cost effective way to achive a high safety Performance Level, and you dont have this feature with any soft-starter.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old October 23rd, 2018, 08:52 AM   #7
JeffKiper
Lifetime Supporting Member + Moderator
United States

JeffKiper is offline
 
JeffKiper's Avatar
 
Join Date: Jun 2006
Location: Indiana
Posts: 2,165
I use soft starts on long ramps and heavy load applications. The data that I have been looking at shows that soft starts can handle a greater amount of overcurrent for a longer time vs a VFD.
__________________
There should be a minimum IQ before people can breed.

FS Eng (TÜV Rheinland, #11004/15, Machinery)
  Reply With Quote
Old October 23rd, 2018, 09:46 AM   #8
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 283
All depends on how hard it is to start the machine.

I used Siemens Sirius starters with 75kW high pressure centrifugal fans that have a very difficult start, the start was smooth, with 30 seconds of ramp and without any belt slip.
__________________
Suppanel HMI
  Reply With Quote
Old October 23rd, 2018, 10:18 AM   #9
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 281
Quote:
Originally Posted by JeffKiper View Post
I use soft starts on long ramps and heavy load applications. The data that I have been looking at shows that soft starts can handle a greater amount of overcurrent for a longer time vs a VFD.
But, you need to watch for motor heat. For a long ramp time, I've used VFD's to actually save energy and reduce motor heat. For instance, a centrifuge, which may require a 2-3 minute ramp. Some motors can't handle it. Since you can ramp the VFD at 100% motor current, there is no overload condition, unlike the Soft Starter, which runs the motor in it's non-linear area of the curve.

On the other hand, there are loads where you need the extra little bit of motor torque to start, and the VFD has to be oversized, where a properly sized, heavy duty Soft Starter can hit a little harder...
  Reply With Quote
Old October 23rd, 2018, 10:30 AM   #10
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 394
When to use a Soft Starter or an AC Variable Frequency Drive
https://literature.rockwellautomatio...p007_-en-p.pdf

Choosing between a soft starter and a variable frequency drive to fit your application
http://www.eaton.com/ecm/groups/publ...ct_1110244.pdf

Last edited by tarik1978; October 23rd, 2018 at 10:33 AM.
  Reply With Quote
Old October 23rd, 2018, 10:19 PM   #11
VAN
Member
United States

VAN is offline
 
Join Date: Apr 2012
Location: Wa
Posts: 228
Quote:
Originally Posted by JeffKiper View Post
I use soft starts on long ramps and heavy load applications. The data that I have been looking at shows that soft starts can handle a greater amount of overcurrent for a longer time vs a VFD.
I always set my SS for current limit instead of the default SS setting. The default actually allows huge current spikes if I remember correctly. But haven't worked on large SS in awhile.
  Reply With Quote
Old October 23rd, 2018, 10:31 PM   #12
JeffKiper
Lifetime Supporting Member + Moderator
United States

JeffKiper is offline
 
JeffKiper's Avatar
 
Join Date: Jun 2006
Location: Indiana
Posts: 2,165
I was starting large saw blades. 120" Diameter. The ramp time was crazy important. If you allowed the system to start in a linear ramp function the blade would hit a harmonic that would cause it to throw carbide inserts. When we let it start with a current limit and it got to through the harmonics much faster. I can't say for sure why the harmonic stayed so long in time based start but it did.
__________________
There should be a minimum IQ before people can breed.

FS Eng (TÜV Rheinland, #11004/15, Machinery)
  Reply With Quote
Old October 24th, 2018, 10:27 AM   #13
dwoodlock
Member
United States

dwoodlock is offline
 
dwoodlock's Avatar
 
Join Date: Nov 2012
Location: South Carolina
Posts: 411
We had an application where a siemens soft start was being used with a 48" centrifugal fan driven by a 25hp motor.

This was my first experience with a soft start, but after the second failure. we ended up replacing it with a very basic siemens VFD. Cost wise the VFD we purchased was about 50% less than the soft start, which was shocking to me.

Luckily the panel had plenty of room so we were able to fit the VFD which was probably 4 times the size of the soft start. Still not real sure why the soft start would periodically go bad. As I recall the first one lasted about 3-4 years and then the second only 2.

When the first one failed we tripped the 250amp breaker that fed the machine. We started noticing strange occurrences around that time before it finally bit the dust. Second time, we started noticing some of the strange occurrences again, and decided to yank it in favor of the VFD after again checking the motor.

VFD has been in service about 9 months now with the same motor and fan without any issues, we'll see if we get better results in the long run.

Anyone ran into something like this?
  Reply With Quote
Old October 24th, 2018, 10:48 AM   #14
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
dwoodlock,
what were the exact type numbers of both softstarter and VFD ?
what were the exact data from the motor name plate ?
what were the "strange occurences" you mention ?
was there a throttle element in front of the fan to ease the startup ?
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old October 24th, 2018, 11:12 AM   #15
dwoodlock
Member
United States

dwoodlock is offline
 
dwoodlock's Avatar
 
Join Date: Nov 2012
Location: South Carolina
Posts: 411
VFD: Sinamics V20 6SL3210-5BE31-8UV0
SS: Sirius 3RW3036-1BB04

Motor: ATB 160L/2F-11S+E3/0703
18kw
460v 60hz 27.4A 3545rpm 0,9 cos theta
IE3 classification

Basically the occurrences were the occasional dimming of lights around the machine, but it would come and go and happened inconsistently. This was 3-4 years ago, so I honestly cant remember everything. I do remember it happened over a few weeks before the soft start finally died out.

Blower is not throttled in any way, basically setup as regenerative with heating elements in its loop.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Less suction pressure on Blower after Star-delta starter replaced by VFD kArTmAN LIVE PLC Questions And Answers 38 October 4th, 2016 12:19 AM
Can use Soft starter for Construction hoist? mindtool LIVE PLC Questions And Answers 5 June 4th, 2012 11:45 AM
VFD as soft starter nightex LIVE PLC Questions And Answers 16 April 24th, 2012 03:45 AM
VFD to Motor Starter nathanht LIVE PLC Questions And Answers 13 July 14th, 2008 03:08 PM
To The Soft Starter Experts BobB LIVE PLC Questions And Answers 2 November 25th, 2004 10:12 PM


All times are GMT -5. The time now is 10:20 AM.


.