Hello
I was needing some guidance on communicating and setting up a totalizer from a flow meter in the PLC.
The PLC is a AB 1769 Compact Logic controller
I’ve never setup a (TOT) Totalizer, but I’m currently communicating to
the Flow meter via 4-20ma out to the PLC input card.
- Do I have to import a new “Data Type” to communicate to the flow meter by Hart?
- Is the best way to setup a Totalizer function in the PLC is to communicate to the meter by Hart?
- Any guidance on setting up the communications & setting up the TOT totalizer would be greatly appreciated.
I attached the TOT instruction from the PLC
- what would need to be configured on this instruction?
- the flow meter is measuring water (Gal/min)
Thanks for helping
The Totaliser instruction doesn't care about HART. In fact, I'd say your challenge is actually finding a Rockwell card for CompactLogix that is HART enabled, unless you look at more expensive or modern IO families.
The scaled value from the meter goes into the In Input of the block and you then toggle the progstartReq bit for it to start totalising for you.
Hi all, I've been using the TOT instruction for totalizing flows wherever I've not had flowmeters with totalizer pulses. It works great and I...
2,052
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
992
SELECTED NEW FILE SELECTED PROCESSOR TYPE SELECTED I/O CONFIGURATIONS IM UNABLE TO CONFIGURE MY I/O’S. I HAVE A PAPER COPY OF A PROGRAM AND I...
103
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
277
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
104