Old March 20th, 2017, 03:57 PM   #16
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 1,778
Quote:
Originally Posted by ceilingwalker View Post
Hello All.
I have a project that is pretty easy however, it involves over 1,000,000 analog inputs. It is a solar panel farm that has 200 inverters, that contain 25 panels each. The customer is requesting Allen-Bradley products, however it is designed. I have never worked with this much I/O in the past and I am hoping someone here has. I am not even sure I want to use a PLC here, since it isn't going to be controlling anything, merely reading data. I am not sure which SCADA system would be best, with this many tags. A one-minute sample rate is all they are requesting. Any and all advice would be greatly appreciated.

Thank you for your time.
The math does not quite add up:

200 X 25 = 5000 panels

1000000 / 5000 = 200 sensors/panel

Do you really need 200 temperature sensors for each panel?!

There are only 200 inverters and each VFD will simultaneously move 25 panels at a time; 5000 analog inputs for defining a single inverter application it is at least a 2 order of power overkill.

IMHO 10000 analog inputs will more than suffice.
  Reply With Quote
Old March 20th, 2017, 04:21 PM   #17
janner_10
Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 198
Pick your local reps brains, let him do the costing for you. Although it does sound quite pie in the sky.
  Reply With Quote
Old March 20th, 2017, 04:30 PM   #18
hoy7t
Member
United States

hoy7t is offline
 
Join Date: Mar 2012
Location: SC
Posts: 66
For that application Mebbe you need one analog input and a lot of multiplexing.
Look at pc data acquisition systems. Rockwell hardware will break the bank for no real benefit.
  Reply With Quote
Old March 20th, 2017, 04:47 PM   #19
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 366
awesome project, if some of those numbers work out. Use proposal works to put a spreadsheet together of cost per point for various AB products, maxing out points per adapter and per PLC. Then have an informed discussing with rockwell about it.

Did they want a complete Rockwell solution, or can you use someone else's SCADA/historian?

SCADA straight to io with AB is either impossible or rare enough that it is not worth persuing. Definitely use a PLC for that bit.
  Reply With Quote
Old March 20th, 2017, 11:39 PM   #20
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,574
Dcs
  Reply With Quote
Old March 21st, 2017, 07:22 AM   #21
Mispeld
Member
United States

Mispeld is offline
 
Join Date: Feb 2017
Location: VA
Posts: 63
While the title indicates "analog inputs" I wonder if the customer literally means 1M physical sensors, or if it is really 1M process variables, some of which may be acquired by communication to inverters or other "smart" devices. In that case, communication protocols may have a significant impact on technology choice.

Even so, I agree the math pointed out in reply #16 still does not add up.
  Reply With Quote
Old March 21st, 2017, 08:16 AM   #22
proof
Member
United States

proof is offline
 
Join Date: Jan 2014
Location: Illinois
Posts: 106
Quote:
Originally Posted by ceilingwalker View Post
I have a project that is pretty easy however, it involves over 1,000,000 analog inputs. It is a solar panel farm that has 200 inverters, that contain 25 panels each.
Wow. I'd say you need to figure out what kind of analog signal you are going to be using. If you used a 4-20 ma signal powered by 24V, 0.02 x 24 x 1000000 = 480 KW. The average home uses about 11,000 KWH. 480 * 24 * 365 / 11000 = 380. If the average signal was 50%, you'd still be using enough power to power 190 homes for just for the inputs. If your signal was a voltage readings the power usage would be much less.
  Reply With Quote
Old March 21st, 2017, 08:37 AM   #23
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 155
Quote:
Originally Posted by proof View Post
Wow. I'd say you need to figure out what kind of analog signal you are going to be using. If you used a 4-20 ma signal powered by 24V, 0.02 x 24 x 1000000 = 480 KW. The average home uses about 11,000 KWH. 480 * 24 * 365 / 11000 = 380. If the average signal was 50%, you'd still be using enough power to power 190 homes for just for the inputs. If your signal was a voltage readings the power usage would be much less.
I don't think that quite works out correctly. 4-20mA signals are powered by 24V, but they don't apply 24V directly across the load (usually approximately a short circuit).

The 4-20mA driver automatically adjusts its voltage to maintain 4-20mA, so the actual voltage across the load is very low.
  Reply With Quote
Old March 21st, 2017, 09:00 AM   #24
proof
Member
United States

proof is offline
 
Join Date: Jan 2014
Location: Illinois
Posts: 106
Quote:
Originally Posted by rupej View Post
The 4-20mA driver automatically adjusts its voltage to maintain 4-20mA, so the actual voltage across the load is very low.
A 4-20 transmitter adjusts its resistance to control the signal current. The voltage drop must match the voltage source, some of the drop is in the input card, and some the transmitter, and some in the wiring. Using a lower voltage source will allow a lower power usage from the system. AB 4-20 ma inputs are 250 ohm. This means the input card with a 20 ma input dissipates 0.02 * 0.02 * 250 = 0.1 Watt. The voltages across the card is 0.02 * 250 = 5V. This is still 100 KW for the system. If the average signal was 50%, then the power usage would be .012 * .012 * 250 = 0.036 Watt (not half as implied in my last post). This is 36 KW, which doesn't include the power used by the transmitter.
  Reply With Quote
Old March 21st, 2017, 09:39 AM   #25
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 155
^Good point- I stand corrected.
  Reply With Quote
Old March 21st, 2017, 11:52 PM   #26
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 656
Quote:
Originally Posted by proof View Post
Wow. I'd say you need to figure out what kind of analog signal you are going to be using. If you used a 4-20 ma signal powered by 24V, 0.02 x 24 x 1000000 = 480 KW. The average home uses about 11,000 KWH. 480 * 24 * 365 / 11000 = 380. If the average signal was 50%, you'd still be using enough power to power 190 homes for just for the inputs. If your signal was a voltage readings the power usage would be much less.
Why has the plant power output gone down 10%?!

Er... we installed a a SCADA system.

This is the first time I've ever thought about the power consumption of analog inputs!!
  Reply With Quote
Old March 22nd, 2017, 04:07 AM   #27
ganutenator
Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: akron, ohio
Posts: 791
Quote:
Originally Posted by ceilingwalker View Post
Hello All.
I have a project that is pretty easy however,...
Every time I hear a project description start this way, pain shoots up my back, I then feel like I am getting electrocuted, then the seizures.
  Reply With Quote
Old March 22nd, 2017, 04:17 AM   #28
Andybr
Member
United Kingdom

Andybr is offline
 
Join Date: Oct 2004
Posts: 558
Quote:
Originally Posted by proof View Post
A 4-20 transmitter adjusts its resistance to control the signal current. The voltage drop must match the voltage source, some of the drop is in the input card, and some the transmitter, and some in the wiring. Using a lower voltage source will allow a lower power usage from the system. AB 4-20 ma inputs are 250 ohm. This means the input card with a 20 ma input dissipates 0.02 * 0.02 * 250 = 0.1 Watt. The voltages across the card is 0.02 * 250 = 5V. This is still 100 KW for the system. If the average signal was 50%, then the power usage would be .012 * .012 * 250 = 0.036 Watt (not half as implied in my last post). This is 36 KW, which doesn't include the power used by the transmitter.
This excludes the actual power supply for the transmitter (if it is a 2 wire device). The actual voltage across the transmitter and the load will be higher. Most 2 wire transmitters require something like 10Vdc to operate correctly which is why cheap loop calibrators with 9V batteries often fail to work correctly.
__________________
“What are the facts? Again and again and again-what are the facts? Shun wishful thinking, ignore divine revelation, forget what “the stars foretell,” avoid opinion, care not what the neighbors think, never mind the unguessable “verdict of history”–what are the facts, and to how many decimal places? You pilot always into an unknown future; facts are your single clue. Get the facts!”

Robert Heinlein.
  Reply With Quote
Old March 22nd, 2017, 11:34 AM   #29
tragically1969
Member
United Kingdom

tragically1969 is offline
 
Join Date: Jun 2007
Location: uk
Posts: 1,124
Are we all sure that the analogue inputs are indeed analogue in the sense of 0-10V or 4-20mA as we know them ?

The OP hasn't specified that and as he says he doesn't get told much, was it a comment in passing "we need to pick up 1000000 points" or "we have to pick up 1000000 4-20mA signals" ? There is a massive difference !

We see specs that detail analogue but in fact just mean anything that isn't digital, if it's just 1000000 data points with a refresh of 1 minute then that's well withing the realms of a well designed PLC/SCADA system.
  Reply With Quote
Old March 22nd, 2017, 12:23 PM   #30
et1ying
Member
United States

et1ying is offline
 
Join Date: Jan 2010
Location: AZ
Posts: 1
Depending on the inverters being used, they may have an Ethernet communication available to view each inverter's data... then no analog inputs required. That would be the best/easiest solution. However, the lack of information from the customer is problematic.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
What is the best solution to interface a large number of analog inputs vigz LIVE PLC Questions And Answers 28 January 24th, 2017 06:12 AM
mV Analog inputs on Profibus/Profinet CharlesM LIVE PLC Questions And Answers 2 April 19th, 2011 06:23 AM
Faster Honeywell HC900 Analog inputs s7killsme LIVE PLC Questions And Answers 1 March 12th, 2011 09:32 PM
cpu314 ifm analog inputs tny LIVE PLC Questions And Answers 3 May 18th, 2007 12:10 AM
analog inputs for RsLogiX 500 tsaronja LIVE PLC Questions And Answers 3 October 2nd, 2006 01:13 AM


All times are GMT -5. The time now is 06:39 PM.


.