Old March 18th, 2017, 01:21 PM   #1
Bering C Sparky
Lifetime Supporting Member
United States

Bering C Sparky is offline
 
Bering C Sparky's Avatar
 
Join Date: Mar 2014
Location: Bering Sea, Alaska
Posts: 955
OSR /OSF in AB

Carry over from another post, but I was asked a question about how AB One Shots functioned on the AD Forum.

Here is the question I was asked:

Quote:
I'm not familiar with AB. Is the one-shot behavior an attribute of the element itself, rather than the instruction?
I answered the question:

Quote:
Yes exactly,
Each One Shot is a unique and individual tag. One Shots become True when the logic before them is True. Not when another instruction with the same tag is True elsewhere in the program.
In Allen Bradley, when a One Shot is placed on a rung, it requires all the instructions before it (to its left) on the rung, to be True in order for the Output to the right of the One Shot to become True for 1 scan.
But then I got to thinking........
I have never used OSR or OSF instructions in AB....only the ONS instruction.

Am I right to assume that the OSR and OSF instructions in Allen Bradley generally follow the same rules as far as, the logic on the rung before the One Shot instruction must be true in the case of the OSR and False in the case of the OSF for the One Shot to become True itself for one scan?

I always assumed that they followed the same general rules as the ONS in this way.

But now I see that AD software acts differently and the One Shot is not a unique tag but replicated from others in the program to function more as a one shot XIC or XIO (Rising / Falling) to a specific tag that is used elsewhere in the program.

Do the OSR and OSF instructions in AB at like the ones in AD also????
Or do they follow the same general rules as the ONS instruction????

I could dig out my old AB software and emulator and try it myself but was hoping someone would just give me the answer for free, so I can put this out of my mind and move on.

Thanks in advance.

BCS
__________________
Changes in Latitude = Changes in Attitude
*********Florida - Seattle - Alaska****************

"I WANT MY LOGIX BACK"

Last edited by Bering C Sparky; March 18th, 2017 at 01:48 PM.
  Reply With Quote
Old March 18th, 2017, 02:26 PM   #2
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,066
I always refer to 'help' documentation on the instruction itself. I have found AB documentation to be fairly though.

Note that a few instructions vary based on the specific family being programmed. Be sure to check that.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com

Last edited by bernie_carlton; March 18th, 2017 at 02:29 PM.
  Reply With Quote
Old March 18th, 2017, 04:00 PM   #3
Doug-P
Member
United States

Doug-P is offline
 
Doug-P's Avatar
 
Join Date: Jun 2003
Location: Pa
Posts: 1,177
Slightly off-topic but, the Click PLC even allows a built in one-shot option for certain box instructions, for example - COPY and MATH. This would allow the elimination of a separate one-shot external to the instruction.

Notice the pulse symbol by the instruction type.
Attached Images
File Type: png Click PLC oneshot.PNG (4.1 KB, 103 views)
__________________
Let's eat Grandma!

Let's eat, Grandma!

Words are very important, but punctuation saves lives...

Last edited by Doug-P; March 18th, 2017 at 04:05 PM. Reason: added graphic
  Reply With Quote
Old March 18th, 2017, 04:26 PM   #4
Bering C Sparky
Lifetime Supporting Member
United States

Bering C Sparky is offline
 
Bering C Sparky's Avatar
 
Join Date: Mar 2014
Location: Bering Sea, Alaska
Posts: 955
Guess I am not getting anything for free today.

No one wants to just give me the answer to the question and are going to make me work for it I guess.

I will look up the answer to my question online or dig out what little software I have for AB later and find out.

Just pulled into Dutch so going to be busy for a while.

BCS
__________________
Changes in Latitude = Changes in Attitude
*********Florida - Seattle - Alaska****************

"I WANT MY LOGIX BACK"

Last edited by Bering C Sparky; March 18th, 2017 at 04:40 PM.
  Reply With Quote
Old March 18th, 2017, 04:45 PM   #5
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 331
ONS: Rung condition out is true for one scan if the rung condition in transitions from false to true.

OSR/OSF: rung condition out = rung condition in.
  Reply With Quote
Old March 18th, 2017, 05:11 PM   #6
Bering C Sparky
Lifetime Supporting Member
United States

Bering C Sparky is offline
 
Bering C Sparky's Avatar
 
Join Date: Mar 2014
Location: Bering Sea, Alaska
Posts: 955
Quote:
Originally Posted by AustralIan View Post
ONS: Rung condition out is true for one scan if the rung condition in transitions from false to true.

OSR/OSF: rung condition out = rung condition in.

Thank you Australian, I appreciate the info.
__________________
Changes in Latitude = Changes in Attitude
*********Florida - Seattle - Alaska****************

"I WANT MY LOGIX BACK"
  Reply With Quote
Old March 18th, 2017, 07:44 PM   #7
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,202
here are some related threads ... if I get time tomorrow (not likely - I'm swamped these days) I'll give you a step-by-step breakdown ... actually it will have to be several breakdowns – because of the variations between the different Allen-Bradley platforms ... anyway - most (if not all) of the different ideas involved are covered in the following threads ...

http://www.plctalk.net/qanda/showthr...0&postcount=10

http://www.plctalk.net/qanda/showthr...27&postcount=4

http://www.plctalk.net/qanda/showthr...2&postcount=13

TIP: following through the continuing conversation presented in the last link above, should go a long way towards convincing you that you're not always going to be able to trust the "books" for subjects like this ... an operational test with the precise equipment is a much more reliable way to nail down the details ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.


Last edited by Ron Beaufort; March 18th, 2017 at 08:08 PM.
  Reply With Quote
Old March 18th, 2017, 11:15 PM   #8
Bering C Sparky
Lifetime Supporting Member
United States

Bering C Sparky is offline
 
Bering C Sparky's Avatar
 
Join Date: Mar 2014
Location: Bering Sea, Alaska
Posts: 955
Hi Ron,
Thanks for the info I appreciate your time.

BCS
__________________
Changes in Latitude = Changes in Attitude
*********Florida - Seattle - Alaska****************

"I WANT MY LOGIX BACK"
  Reply With Quote
Old March 19th, 2017, 11:44 AM   #9
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,202
I'm pretty sure that your main issue is that there are differences between how the Automation Direct software handles One-Shots - and how the Allen-Bradley software handles them ... what makes it even more challenging is that there are quite a few differences between how they get handled just by the various Allen-Bradley platforms ...

anyway - before you move on, you'll certainly want to consider how the "retentive" Latch/Unlatch instructions in Allen-Bradley differ from the Set/Reset instructions in Automation Direct systems ... many people think that these are directly interchangeable ... they are NOT ... and quite a few safety issues can arise when these are misused by programmers who don't really understand the differences ...

the following link should help ...

http://www.plctalk.net/qanda/showthr...86&postcount=1

man - has it been 12 years since I wrote that? ... it seems like yesterday ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old March 19th, 2017, 07:33 PM   #10
Bering C Sparky
Lifetime Supporting Member
United States

Bering C Sparky is offline
 
Bering C Sparky's Avatar
 
Join Date: Mar 2014
Location: Bering Sea, Alaska
Posts: 955
Ron,

I know I have read this post before, but its been years ago.
Now that I am actually working with Automation Direct devices it was good to read this again.

As always your post are very informative and helpful.

Thanks again,
BCS
__________________
Changes in Latitude = Changes in Attitude
*********Florida - Seattle - Alaska****************

"I WANT MY LOGIX BACK"
  Reply With Quote
Old March 20th, 2017, 12:05 PM   #11
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 748
Quote:
Originally Posted by Ron Beaufort View Post
the following link should help ...

http://www.plctalk.net/qanda/showthr...86&postcount=1

man - has it been 12 years since I wrote that? ... it seems like yesterday ...
Just reread it, surprised to find my first post in that thread. It's been a while...
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSLogix 500 one shot vs RSLogix 5000 one shot Prayder LIVE PLC Questions And Answers 5 December 29th, 2014 05:50 PM
ONS vs OSR Narlin LIVE PLC Questions And Answers 7 March 4th, 2013 04:21 PM