Serial Port on the Logix 5562 to RS-485
I have a 5562 that I need to attempt to connect to a RS-485 Emerson Drive. The issue I have is that I can't for the life of me find the pinout.
Also, is this possible without a converter? I remember needing to use an adapter with other PLCs. I need it to do Modbus-RTU. I will be getting the ProSoft (4 ports needed if you believe it) cards with the new PLC when it comes in, but I need to use this old one for the time being. Thanks in advance. |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
You will need an 1761-NET-AIC converter to connect the L62 controller Serial port to a RS-485 network.
http://literature.rockwellautomation...m004_-en-p.pdf For using the L62 controller as a Modbus Master/Slave device follow http://literature.rockwellautomation...p129_-en-p.pdf Modbus applications examples are part of the RSL5k/Studio 5000 install Samples folder. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Feb 2017
Location: Pennsylvania
Posts: 27
|
Thanks. That's what I feared.
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Oct 2010
Location: Venezuela
Posts: 660
|
Just curious: Why do you need 4 ports?
__________________
"If you can't solve a problem, then there is an easier problem you can solve: find it." (George Pólya) |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Feb 2017
Location: Pennsylvania
Posts: 27
|
I need 4 ports because there are 4 drive controllers. The response time for serial communications is too low. Of course if we just added the Ethernet/IP modules to the controllers would could save something like $8k per system these go into.
|
![]() |
![]() |
#6 |
Lifetime Supporting Member + Moderator
|
You will probably not be satisfied with the response time of the Modbus/RTU sample code for the 1756-L6x serial port, especially if you're daisy-chaining it to multiple devices.
How many read/write registers to you need to do per Emerson controller ? If you just need to do a few, and you don't mind spending a little time experimenting with configuration, the GridConnect NET485 is the most cost-effective way to connect a handful of Modbus/RTU serial registers to a ControlLogix over Ethernet. It only addresses one slave device, but it's $100 retail. And once you get the configuration file figured out, you just load it via TFTP and you're done. |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Oct 2010
Location: Venezuela
Posts: 660
|
Why don't you connect the drivers in a dasy-chain?
The response time will be an issue if you intend to control the speed using a PID from the controller. In similar configurations, I use the internal driver's PID and set the speed from the PLC. Of course, I don't know if that's possible in your application.
__________________
"If you can't solve a problem, then there is an easier problem you can solve: find it." (George Pólya) |
![]() |
![]() |
#8 |
Member
|
Check out the Prosoft card.
__________________
"Keep it simple." |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Feb 2017
Location: Pennsylvania
Posts: 27
|
I'm getting two of them. I just don't have them, or the PLC I need yet and want to keep writing code.
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
PV600 comm problem | RickParrot | LIVE PLC Questions And Answers | 28 | January 23rd, 2016 06:02 AM |
Is RS Linx still on and loaded with the RS Logix 5000 CD ? | Rob S. | LIVE PLC Questions And Answers | 5 | October 21st, 2014 03:24 PM |
Control Logix 1756-L55 Serial Port Fault | bob1371 | LIVE PLC Questions And Answers | 0 | April 29th, 2014 01:22 PM |
Compact Logix Serial Port Diagnostics | plcnovel | LIVE PLC Questions And Answers | 0 | October 19th, 2006 12:51 PM |
Need PLC to control via serial port ... | LIVE PLC Questions And Answers | 9 | February 28th, 2003 07:01 AM |