Old February 11th, 2009, 03:51 PM   #16
Chance85
Member
United States

Chance85 is offline
 
Join Date: Apr 2005
Location: Mid South
Posts: 55
Was there a reason why you couldnt' just change the battery? I'm just wondering why he would have you clear the memory when the only problem was a dead battery.

Last edited by Chance85; February 11th, 2009 at 03:55 PM.
  Reply With Quote
Old February 11th, 2009, 04:02 PM   #17
Stgmavrick
Member
United States

Stgmavrick is offline
 
Join Date: Feb 2009
Location: Ohio
Posts: 8
Sorry, the battery was replaced first. When the processor didnt come back, then unplugged the battery and then shorted the pins.
  Reply With Quote
Old February 11th, 2009, 05:23 PM   #18
Chance85
Member
United States

Chance85 is offline
 
Join Date: Apr 2005
Location: Mid South
Posts: 55
Were you testing these units in the same backplane? If so you might want to try another if you have one available. I have seen simular problems with faulty backplanes/powersupplies. Just a thought.
  Reply With Quote
Old February 11th, 2009, 06:24 PM   #19
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,112
I'm sure you are being as accurate as you can, but there's something that seems wrong about this story.

The RAM backup batteries in SLC-5/0x controllers will generally last for two years with the power off. With the power on, they can last indefinitely; I have seen ten year old controllers with good batteries, though self-discharge life can be as short as 4-5 years in a hot environment.

The SLC operating system OS501 Series C FRN 9 was released in November 2004, so the oldest these controllers could be is about 4 years. If they've been powered up most of the time, they are on the short end of battery lifespan.

What's indisputable is that the controller should not lose its program when it is powered off and the battery removed long enough to install a new battery. The capacitor will retain the user program for days, weeks, sometimes months.

So what we have is controllers that have failed batteries in a relatively short period of time and displayed uncharacteristic behavior before diagnostic work began.

That, to me says damage. Lightning damage, humidity damage, heat damage, ESD damage, don't know what kind. But firmware is bringing up the very back of the parade on the list of things I'd be looking at in these controllers.
  Reply With Quote
Old February 11th, 2009, 06:51 PM   #20
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,112
Quote:
According to my rep, there are 0 replacement processors available.
Maybe your guy is making a very nearrow inquiry, like checking only for remanufactured units or a specific old hardware version. I can't imaging he's lying, but we might be talking about different questions.

Quote:
What i've decided i'm going to do is purchase 2 series A replacements and purchase the firmware upgrade to upgrade them to C. It will save some money and my customer will have his replacements.
SLC controller revisions can be a little bit confusing because there are Series letters both for the hardware and the operating system.

Currently manufactured controllers are Series C hardware and also have the OS501 Series C operating system in them.

Series C hardware introduced the 10/100 Mb/s Ethernet daughtercards, and was introduced at the same time as OS501 Series C FRN 9 firmware in November 2004.

You can load the current firmware, which is OS501 Series C FRN11, into any SLC-5/05 controller ever made, no matter if it's Series A, B, or C hardware. You won't get 100Mb/s hardware performance in the old controllers, but you will get all the other features and functions of the current operating system.

You should not be able to purchase Series A hardware SLC-5/05 controllers from any A-B distributor because they have not been manufactured in nearly a decade.

My guess, based on the information you have provided, is that the same damage will befall the replacement controllers that affected the originals.
  Reply With Quote
Old February 12th, 2009, 08:58 AM   #21
Stgmavrick
Member
United States

Stgmavrick is offline
 
Join Date: Feb 2009
Location: Ohio
Posts: 8
To answer some of your questions.

Chance, The processors were brought back to our office to test in a separate rack to test the same theory. While they were moved around to the different racks at the plant they were installed in, we still felt using a rack/powersupply from a different environment was a good idea. Our test rack performs the same as the racks in the field.

Yes, these controllers have been installed and running every day for about 4 years. The batteries were showing bad which is why we went to replace them.

Yes, we were looking at remanufactured processors. I should have clarified as it caused confusion.

I am aware of the performance difference, however the system that these processors are running does not utilize that communication speed and it can be sacrificed.

I am also aware that series a and B are not currently available new, however we'll be purchasing a used one at a far lower cost than what rockwell charges to repair a bad processor.

I had the same assumption you had yesterday; That these processors were toast. With that known, i repeatedly shorted pins followed by a power up retest over and over and I was able to get one working again. This processor is running and continues to run as we speak regardless of power cycle. Yesterday after i was able to get it to run and communicate a cycle of power would have a 50/50 chance of solid fault or running the test program. This is not the case now, i've been unable to get a solid fault after letting it run all night. I've tried duplicating the issue and am unable to do so after 24 hours of testing. I'll let it run at my bench for another week peridically cycling power before i make a decision as to replace it or not.

Yesterday when I was able to get the processor to communicate and run for a couple hours and then solid fault again after i cycled power, i started thinking that whatever problem these processors share was not caused by replacing the battery. I think that whatever happened it happened prior to the battery replacement and powering it off triggered it. It reminds me of a computer OS who's start up routine is damaged. Sometimes it will come up, sometimes it wont; however, once it is running, it stays running.

The second controller is a different story. I did find out a little more information this morning. I was able to talk with the programmer who originally changed the batteries. While he was on the phone with Rockwell, one of their agents asked him to move the firmware jumper to "PROGRAM" to see if the light pattern changes. Because of this, i think this processor does not have a firmware loaded anymore. This would confirm as to why shorting the pins has no effect. Cant restore default settings for software that doesnt exist. Either way, the firmware upgrade kit is on its way so who knows, maybe it will work.

I just find it odd after all my years working with electronics that 2 units go bad at the same time the exact same way. This wouldnt suprise me if it was a common issue, however Rockwell states there are no known documented cases that match this issue. Thats why I posted here. I wanted to see if others have had this issue and that Rockwell is denying it. It wouldnt be the first time. Control logix L55's

Last edited by Stgmavrick; February 12th, 2009 at 09:05 AM.
  Reply With Quote
Old February 12th, 2009, 02:48 PM   #22
rta53
Lifetime Supporting Member
United States

rta53 is offline
 
rta53's Avatar
 
Join Date: Feb 2003
Location: North Carolina
Posts: 602
We installed a system for one of our customers in Sept. of 2005. It has a 5/05 processor and last year the customer had to replace the processor because the original processor lost the program. They tried downloading the program again but basically it kept dissapearing so they replaced the processor. I had not seen this before. I thought about it because it sounded similar to the issue Stgmavrick is having. I believe their processor started losing the program after a power loss also.
  Reply With Quote
Old February 16th, 2009, 04:06 PM   #23
spice_miner
Member
United States

spice_miner is offline
 
Join Date: Aug 2006
Location: Iowa
Posts: 45
Blinkers

Is this what it's doing??

http://www.youtube.com/watch?v=sMMEW68AhMg
  Reply With Quote
Old February 16th, 2009, 04:31 PM   #24
Stgmavrick
Member
United States

Stgmavrick is offline
 
Join Date: Feb 2009
Location: Ohio
Posts: 8
Nope, sorry.

The fault light stays solid red. Battery will flash once. Then Batt, force, enet, and rs232 lights will flash once, then it will repeat.
  Reply With Quote
Old July 7th, 2009, 09:45 AM   #25
kooch1221
Member
United States

kooch1221 is offline
 
Join Date: Jul 2009
Location: New York
Posts: 1
Ive had the same issue with at least 5 units on one of my projects. They have all failed in the manner described above. Most have failed during a download or online update using the Enet port.
  Reply With Quote
Old September 12th, 2009, 07:52 AM   #26
pskillen
Member
United Kingdom

pskillen is offline
 
Join Date: Sep 2008
Location: UK
Posts: 6
Did anyone have any luck with this? I've just had the same problem with a 5/03 I bought second hand. The problem may or may not have been caused by me starting it up with J4 in "program" but not actually performing an upgrade. The processor works fine straight after a factory reset, but after a power cycle it goes back to flashing away at me angrily
  Reply With Quote
Old September 12th, 2009, 07:09 PM   #27
rguimond
Lifetime Supporting Member
Canada

rguimond is offline
 
Join Date: Jul 2009
Location: Escuminac
Posts: 610
If you're REALLLY desperate, I can overnight a new procesor to you on Monday. Just PM me with your coordinates and we'llmake arrangements for payment / replacement.
__________________
"If you can't measure it, you can't manage it!"
  Reply With Quote
Old September 15th, 2009, 01:29 PM   #28
rta53
Lifetime Supporting Member
United States

rta53 is offline
 
rta53's Avatar
 
Join Date: Feb 2003
Location: North Carolina
Posts: 602
Quote:
Originally Posted by Ken Roach
The RAM backup batteries in SLC-5/0x controllers will generally last for two years with the power off. With the power on, they can last indefinitely; I have seen ten year old controllers with good batteries, though self-discharge life can be as short as 4-5 years in a hot environment.

What's indisputable is that the controller should not lose its program when it is powered off and the battery removed long enough to install a new battery. The capacitor will retain the user program for days, weeks, sometimes months.

So what we have is controllers that have failed batteries in a relatively short period of time and displayed uncharacteristic behavior before diagnostic work began.

That, to me says damage. Lightning damage, humidity damage, heat damage, ESD damage, don't know what kind. But firmware is bringing up the very back of the parade on the list of things I'd be looking at in these controllers.

You say that the capacitor can maintain a program in RAM for weeks or even months. However the hardware manual says this:

"The SLC 5/03, SLC 5/04, and SLC 5/05 processors have a
capacitor that provides at least 30 minutes of battery back-up
while the battery is disconnected. Data in RAM is not lost if the battery is replaced within 30 minutes."


Granted they are probably being conservative about this but I wouldn't want to go days without a battery. If you look at my earlier post I mention a customer having to replace a 5/05 processor because it would not hold a program. Well the same thing happened again just last week after they had a Labor Day shutdown. I'm not sure how long the system was off but when they tried to power the system back up there was no program in the processor. They were able to download the program and resume operation but a few days later the processor faulted and this time they could not download. They kept getting a message that the program was incompatible with the processor. They replaced the processor and were then able to download. I really don't know what's going on with this system but 2 processors in 4 years is not good. I have not seen this with any other SLC system we have installed in the last 15 years.

  Reply With Quote
Old July 18th, 2010, 06:00 PM   #29
N_ubalde
Member
Philippines

N_ubalde is offline
 
N_ubalde's Avatar
 
Join Date: Sep 2008
Location: Muntinlupa
Posts: 3
Ive had the same issue which happens after a power switch-over from the grid to gensets.
  Reply With Quote
Old July 22nd, 2010, 10:48 AM   #30
jtorres2_77
Member
United States

jtorres2_77 is offline
 
Join Date: Feb 2006
Location: chicago
Posts: 63
If the slc processor keeps rebooting then the unit usually needs repair. I have repaired hundreds of these processors in the past. For a much cheaper repair then the OEM send me an e-mail. jtorres2_77@hotmail.com
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB SLC 5/05 Ethernet MSG Errors mrdegold LIVE PLC Questions And Answers 7 January 20th, 2009 12:10 PM
Strange fault on SLC 5/05 system. 93lt1 LIVE PLC Questions And Answers 11 June 1st, 2006 03:02 PM
SLC 5/05 Ethernet hardware fault (A2h) Znatok LIVE PLC Questions And Answers 2 October 11th, 2005 11:26 AM
SLC 5/05 fault no RSLogix Matthias von Zorn LIVE PLC Questions And Answers 19 May 28th, 2003 08:51 AM
SLC 5/04 fault???? john paley LIVE PLC Questions And Answers 9 February 7th, 2003 06:59 PM


All times are GMT -5. The time now is 09:35 AM.


.