VFD controls

Rson

Member
Join Date
Jun 2017
Location
Michigan
Posts
520
So, I have a customer with a VFD system - pretty simple single VFD (Emerson) - and he wants us to just send direct signals from the PLC output to the VFD drive. (VFD is in another room)

I've always used interposing relays with the VFD's control power to drive VFD I/O - it is just how things were done everywhere I have been.

Are there any disadvantages you have seen to using a sourcing output from a PLC into a VFD's digital input? Shouldn't I isolate these signals somehow?
 
You will need to check the drive data but these inputs are sometimes already isolated through opto-isolators. If all the inputs come from one source the input common simply becomes the source common and the inputs go straight in. It just gets tricky when you are tying together commons from multiple sources.

Keith
 
Nothing wrong with using the PLC's 24V instead of the drive's. Much easier to do multiple drives that way.
 
we always use a contact closure to start / stop the drive.
you should also use an operator start/stop/estop at the drive.
you will need a disconnect at the drive since the drive is in another room.

what is the vfd voltage and the distance from the drive to the motor?
you may need to include line and load reactors.

james
 

Similar Topics

I am looking for some pointers on setting up a VFD (PowerFlex70 in this case) to operate beyond normal operation. -Low speed without overheating...
Replies
23
Views
6,818
My DeviceNet skills are rusty and weak... so of course, an old, obsolete Reliance 400 HP VFD goes down and we're looking at replacing it with a...
Replies
7
Views
4,983
Since I'm sure many have done this here and this is actually my first time controlling a pump, I hope I could get some opinions from everyone. I...
Replies
10
Views
3,804
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
115
Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
Replies
2
Views
149
Back
Top Bottom