Old July 17th, 2017, 05:44 AM   #1
Vadagor
Member
Spain

Vadagor is offline
 
Join Date: Jul 2017
Location: Barcelona
Posts: 17
S7-1200 to KTP HMI Addressing

Hello everybody,

I will need to change IP addresses on some PLC´s and HMI´s. I found how to change the PLC addresses (s7-1200tools) and the HMI addresses (through their touch panel menú). My question is, where do I change the "PLC address" inside the HMI? Because I can imagine that, like in Schneider systems, if I change IP addresses, the HMI won´t know where to find the required information from. Any suggestion?

Cheers,

Nick.
  Reply With Quote
Old July 17th, 2017, 08:28 AM   #2
boneless
Lifetime Supporting Member + Moderator
United States

boneless is offline
 
Join Date: Feb 2008
Location: OKC
Posts: 1,227
I don't know of any way of doing this, besides in the engineer software.
  Reply With Quote
Old July 17th, 2017, 09:48 AM   #3
dwoodlock
Member
United States

dwoodlock is offline
 
Join Date: Nov 2012
Location: South Carolina
Posts: 295
I think you will likely have to use portal to change the plc IP address. Unless perhaps you can change system block parameters from a mmc, which I have no idea about. My want to inquire with siemens
  Reply With Quote
Old July 17th, 2017, 09:50 AM   #4
Patrix
Member
Netherlands

Patrix is offline
 
Patrix's Avatar
 
Join Date: Aug 2011
Location: Enschede
Posts: 98
If your lucky, power down the panel and power on, then there should be a load screen with three options. I think it was start, tranfer and config. hit config and you can change the IP adres. But you need to tell the PLC on what adress the panel is
  Reply With Quote
Old July 18th, 2017, 01:58 AM   #5
Vadagor
Member
Spain

Vadagor is offline
 
Join Date: Jul 2017
Location: Barcelona
Posts: 17
Quote:
Originally Posted by boneless View Post
I don't know of any way of doing this, besides in the engineer software.
As the work will be done by unexperienced technicians, this is what I want to avoid, to use a "complex" piece of software. Thanks anyway!
  Reply With Quote
Old July 18th, 2017, 01:59 AM   #6
Vadagor
Member
Spain

Vadagor is offline
 
Join Date: Jul 2017
Location: Barcelona
Posts: 17
Quote:
Originally Posted by dwoodlock View Post
I think you will likely have to use portal to change the plc IP address. Unless perhaps you can change system block parameters from a mmc, which I have no idea about. My want to inquire with siemens
Same here. Technicians on site don't have enough experience with TIA so I don't want them to mess around.

Cheers, mate!
  Reply With Quote
Old July 18th, 2017, 02:02 AM   #7
Vadagor
Member
Spain

Vadagor is offline
 
Join Date: Jul 2017
Location: Barcelona
Posts: 17
Quote:
Originally Posted by Patrix View Post
If your lucky, power down the panel and power on, then there should be a load screen with three options. I think it was start, tranfer and config. hit config and you can change the IP adres. But you need to tell the PLC on what adress the panel is
Yes, this was my first option but, when I checked the procedure, I found how to change the HMI Panel IP address but not the host PLC IP address.
I also saw a new document (but just for KTP700) where it says how to configure this PLC IP address, but the interface looks a bit different from the old one (which is present on my site).

I will keep looking, and praying.

Thanks!!
  Reply With Quote
Old July 18th, 2017, 04:39 AM   #8
Kelkoon
Member
Spain

Kelkoon is offline
 
Join Date: Dec 2004
Location: Spain
Posts: 131
Hi,

There is a tool called that may help you: SIMATIC Automation Tool

It allows you to change the PLC address.

Best regards,
kelkoon
  Reply With Quote
Old July 18th, 2017, 09:16 AM   #9
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,367
Quote:
Originally Posted by Kelkoon View Post
Hi,

There is a tool called that may help you: SIMATIC Automation Tool

It allows you to change the PLC address.

Best regards,
kelkoon
The SAT allows you to change the PLC IP address. However, OP has already done that. What he wants to do is change the address that the HMI is configured to connect to.

I know that the HMIs have a "ChangeConnection" system function that you can add to a button, do those work with 1200's? I could have sworn that I'd used them before, but when I just tested it, the function only seemed to support S7300/400 connections.
  Reply With Quote
Old July 18th, 2017, 09:21 AM   #10
boneless
Lifetime Supporting Member + Moderator
United States

boneless is offline
 
Join Date: Feb 2008
Location: OKC
Posts: 1,227
Now I think of it, I recently did something similar, by creating a USB back-up in my office. Set up an identical screen with the correct IP info, backed it up to a USB stick and sent it to a client. He then restored the screen from the back-up.

Draw back is that you need an identical screen to do this.

Alternatively, when my techs are out and don't know what/how to do things, I often use teamviewer to do the work through their PC.
  Reply With Quote
Old July 19th, 2017, 12:56 AM   #11
Vadagor
Member
Spain

Vadagor is offline
 
Join Date: Jul 2017
Location: Barcelona
Posts: 17
Thank you everybody for your suggestions! I think I will try what boneless mentioned about having a backup inside a USB and do the work offline.

Thanks!!!

Nick
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How to use a General PC as HMI + PLC S7 1200 + TIA v.13 mihesper LIVE PLC Questions And Answers 1 December 4th, 2016 07:38 AM
HMI - Issues setting up indirect addressing BennieC LIVE PLC Questions And Answers 11 August 20th, 2016 04:58 PM
S7 1200 (4 PLC's & 4 HMI) boneless LIVE PLC Questions And Answers 1 April 21st, 2016 11:46 PM
s7 1200 to scada rQx LIVE PLC Questions And Answers 9 October 26th, 2011 11:07 AM
s7 1200 , HMI Alarms rQx LIVE PLC Questions And Answers 4 December 15th, 2010 05:41 PM


All times are GMT -5. The time now is 01:31 PM.


.