Hi All, Ive an SLC program that messages to several other slc 505s as well as a positrack system. The SLC explicit messages the positrack every .02 seconds. Ive noticed that my other messages can occasionally behave strangely. The message will be enabled, but it never times out, finishes, errors, nothing. The diagnostic file doesnt seem to indicate any problems either. It just sits there. Flipping the plc from run to program and back makes the messaging work again. It seems to be tied to the explicit messaging. I changed the explicit message so it it only does the explicit messaging when it actually needs the data, and so far it seems to have helped. So, my question is, can explicit messaging override normal MSG commands (ive never had to use explicit messaging before). Thanks