i am using modbus pol to trouble shoot a modbus comms issue. I have device communicating modbus over rs485 going through a lantronix express DR which convert is to modbus over tcp/ip. I can read the data fine on the rs-485 side and to the best of my knowledge the Lantronixs is setup correctly??? I dont have the software to check it. But when i connect modbus pol to the ethernet side I get Insufficient bytes received? I have tried multiple setting in modbus pol with no luck. I have the correct IP as I can ping the lantronix. I am leaning toward a lantornix config issue, but I have little experience with these devices so I was wondering what that error message even means. MOdbus pol gives no explanation in the users manual. Thank you for any advice!! Also is there somewhere online where you can download the lantornix software as I dont have access to the DVD? tired there webs site with no luck.
  Reply With Quote
Old September 14th, 2021, 02:43 PM   #2
diat150
Lifetime Supporting Member
United States

diat150 is offline
 
Join Date: Mar 2006
Location: Louisiana
Posts: 1,381
you should be able to telnet into the lantronix using the ip and port 9999


I dont think the express dr supports modbus tcp, you would need to use modbus rtu over tcp/ip in modbus poll. But first things first, you need to check all of the settings.
  Reply With Quote
Old September 14th, 2021, 03:23 PM   #3
Lare
Member
Finland

Lare is offline
 
Join Date: Jan 2006
Location: Finland
Posts: 1,664
Quote:
Originally Posted by diat150 View Post
you should be able to telnet into the lantronix using the ip and port 9999


I dont think the express dr supports modbus tcp, you would need to use modbus rtu over tcp/ip in modbus poll. But first things first, you need to check all of the settings.

Thinking same, it is modbus rtu over TCP not Modbus TCP.


There is virtual com port software for PC. (You setup your PC to connect virtual com port it then redirects rtu querys to lantronics ethernet port if your client don't support modbus rtu over TCP protocol directly.)



Download link and setup software links are here:

https://www.lantronix.com/products/x.../#tab-overview
  Reply With Quote
Old September 14th, 2021, 03:38 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,049
I think the important distinction is "Modbus / TCP" versus "Modbus RTU encapsulated over TCP/IP".

Ethernet/Serial gateways that are "Automation protocol enabled" generally run real Modbus/TCP protocol on the Ethernet side. They receive a Modbus/TCP command, break it up into its component parts, and then send it out the serial side as a Modbus RTU command.

But there are also cheaper and simpler Ethernet/Serial gateways that don't know anything about industrial automation protocols. They just implement a "virtual serial port", and encapsulate the whole serial string or protocol frame instead of translating or interpreting it.

Lantronix "DR" are their Din Rail mounted gateways, of course. But they offer two nearly identical models: "XPress DR" and "XPress DR-IAP".

If you've got an XPress DR-IAP, then setting up your Modbus Poll for Modbus/TCP mode is correct.

But if you've got an XPress DR, then you need to set up Modbus Poll as though it was running Modbus RTU protocol over a virtual serial port, and get that virtual serial port configured using LanTronix tools.
  Reply With Quote
Old September 14th, 2021, 04:13 PM   #5
RY_Guthrie
Member
United States

RY_Guthrie is offline
 
Join Date: Nov 2011
Location: Las vegas, NV
Posts: 245
software

Unfortunately i dont have the install disc for the lantronix software so I am using the web interface. It is a xpress DR going by the id panel on the side. I just got the web browser working. I have not figured out what parameters are important and what ones are not. Its a new piece of equipment for me so I am having to read the manual. Thank you to every one who responded, this site has helped me more times than I can count!!
  Reply With Quote
Old September 15th, 2021, 03:37 AM   #6
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 660
Maybe you have a problem with the RS-485 flow control, maybe the Lantronix module switches to receive mode too late and bytes are lost.

Do you know if the missing bytes are from the beginning or the end of the slave reply ?
__________________
Suppanel HMI
  Reply With Quote
Old September 15th, 2021, 08:40 PM   #7
Psnikta
Member
Australia

Psnikta is offline
 
Join Date: Mar 2020
Location: QLD
Posts: 15
The "Insufficient bytes received" message is probably because it is missing the MBAP header (7 bytes long)...


Does modbus pol display the messages in HEX?
  Reply With Quote
Old September 16th, 2021, 04:55 AM   #8
tragically1969
Member
United Kingdom

tragically1969 is offline
 
Join Date: Jun 2007
Location: uk
Posts: 1,544
I have nothing else to add apart form what Ken Roach said! You won't get anything on Modbus TCP from the DR model.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Modbus Poll communication setting? PLC1234 LIVE PLC Questions And Answers 6 November 16th, 2020 05:12 PM
S7-1500 Modbus RTU Poll Interval Hal9000 LIVE PLC Questions And Answers 4 August 23rd, 2020 04:23 PM
Ethernet TCP/IP and Allen-Bradley CompactLogix (RSlogix 5000) CAAJ LIVE PLC Questions And Answers 14 December 18th, 2015 12:46 PM
Modbus Master not polling the Modbus Slave through an EtherNet/IP Connection mihiri LIVE PLC Questions And Answers 3 July 15th, 2010 03:41 AM
Mitsubishi Q Series Modbus TCP module QJ71MT91 set up help req'd... Pocko LIVE PLC Questions And Answers 0 July 30th, 2006 03:45 AM


All times are GMT -4. The time now is 08:46 AM.


.