Panelview Inactivity Screen Control

Join Date
Feb 2005
Posts
2
Looking for some help on a PV1000 display. I was wondering if anyone has transfered the currently displayed screen (if secured) with an unsecured screen after some ammount of time of inactivity on the secured screen. I know about the control and status tags in the panelview so I can transfer or control which screen is displayed just wondering if someone migh have a trick, short of me adding a bunch of additional logic to reset PLC timers each time a button or value is changed on a secured screen. Thought I might be able to use the screen saver feature but the tag that tells whether the panelview is in screen saver mode appears to be internal to the panelview only, and not available for writing to the PLC. Let me know if you have anything that may be useful. Thanks in advance.
 
You mean like "Secure on Idle"

There's a checkbox on the Security configuration (Menu | Application | Security) for "Secure on Idle".

Per the help file:
If idle mode is enabled, the terminal logs off the current operator and returns to the startup screen (if the current screen is secured).

Allen-Bradley Company, LLC, Copyright © 1993-2002, All Rights Reserved

Is this what you are looking for?
 
I beleive so????

I thought I looked through all the configuartion menu's etc, but what I didn't relize is that because I am using a PanelView firmware version 3.30 the security feature is not available. I just need to get my firmware updated and I beleive your suggestion will work great. Thanks for the help in the right direction.
 

Similar Topics

Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
127
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
64
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
92
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
80
Can anyone help out with this Panelview Plus Performance Email. I keep getting an "unable to activate connection "smtp-mail.outlook.com". I've...
Replies
4
Views
202
Back
Top Bottom