Thanks everyone for your responses, especially jrwb4gbm for giving me the link for the manual. Let me tell you what occured and se if you all shake your heads in disbelief also. We have a machine which quit working this morning. The operator said that she felt an electrical shock when she touched the frame. So being the safety minded person that I am, I checked the chasis ground. Know what? Ground wire was conected to the neutral bus instead of to chasis. Tried to ohm out chasis to neutral and correctly no continuity. Found a 120V heating element shorted to ground, there explains the shock. No way to ground out and blow fuses when there is no ground conected. Corrected problems, machine will not run because the plc is showing an error. Well ****, not familiar with an Idec so what does the error mean? Probably not good knowing my luck though. I finally talk to Idec tech support (they were great) and they said to pull the EEProm and put it into an identical machine and see if it runs, also reiterated not to put the EEProm from good plc into bad plc. If the known good plc ran with suspect plc EEProm then it would be a bad cpu. Tried the swap and known good plc ran fine. I was convinced the cpu was fried. I put the original EEprom back into the bad plc and you know what? The damn thing ran fine......Oh well occasionally I do get lucky.
dale